Choice of CT in SubStation

03/07/2011 7:14 AM

For a substation where live tank/dead tank CT will be selected and why?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor
India - Member - New Member

Join Date: Feb 2011
Posts: 14
#1

Re: Choice of CT in SubStation

03/08/2011 12:53 AM

Following are the advantages of Live Tank over dead Tank :

a) The Primary conductor is short than (in live tank CT) than the Dead tank CT which gives better Rigidity and gives high short circuit current withstanding capability and reliability.

b) Primary winding is uniformly distributed around Core, Hence CT is truly low reactance type, which has inherent better transient performance.

c) Due to shorter length and the tank being live the major insulation is not over the high current carrying primary, which is the main source of heat (as in the case of Dead tank type design.) the insulation does not get heated up while dissipating the heat generated. This facilitates much superior thermal stability of insulation and longer life.