I'm sure this has been discussed before, but I was just curious since I've seen several ideas and methods regarding panelboard ampacity ratings and sizing methods.
The method I most often see is to divide all two and three-phase loads evenly on the phases, sum the connected kVA's per phase and find their associated amperes per phase, and then size the panelboard and main breaker if necessary accordingly by the highest phase ampacity you require. The transformer feeding the panel if necessary is sized per the total kVA that you see on the panel (i.e. all three phases summed). Obviously it is advantageous to balance the loads as evenly as possible to keep both the panelboard rating and transformer size down.
How about you?