3 Phase Induction Motor Cable Rating and Overload Rating

03/14/2011 11:36 AM

Could you please provide me with the above details in tabulated form for a range of motors or for a 15kw 380V ac motor?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#1

Re: 3 Phase Induction Motor Cable Rating and Overload Rating

03/14/2011 12:04 PM

15kW 380V induction motor will take approximately 30Amp. Refer tables or cataloque for accurate result. If wye delta starter is used OL setting can be 30 divided by 1.732. For cable size you should give ambient temperature,type of cable(armoured/ unarmoured/ clipped to surface/enclosed in conduit/buried/single or grouped etc)

__________________
pnaban
Reply Score 1 for Good Answer
Anonymous Poster #1
#2
In reply to #1

Re: 3 Phase Induction Motor Cable Rating and Overload Rating

03/15/2011 2:32 AM

15kW 380V induction motor will take approximately 30Amp. Refer tables or cataloque for accurate result. If wye delta starter is used OL setting can be 30 divided by 1.732. For cable size you should give ambient temperature,type of cable(armoured/ unarmoured/ clipped to surface/enclosed in conduit/buried/single or grouped etc)

It's direct on line starter, the cable should be armoured running on a cable tray grouped, ambient tempaerature about 20 degrees celcius, so what would the cable size and overload setting be?Or if there is a standard reference table may you please forward it to me

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#3
In reply to #2

Re: 3 Phase Induction Motor Cable Rating and Overload Rating

03/15/2011 6:49 AM

If you are in a Commonwealth country refer BS 7671(IEE wiring regulations). Otherwise refer NEC or equivalent relevant to your country

__________________
pnaban
Reply Score 1 for Good Answer