2 Phase Load on 3 Phase Alternator

03/15/2011 2:25 PM

Hi All !

I have a curious question which I am facing in real life. I need to feed 250A from a

diesel generator set to an equipment under test for 8 hours.

Now, the catch......

The load is only 2 phase and the generator is 500 kVA, 3 phase 4 wire.

Is it safe to load the DG set for such a long period with 250 Amps current in 2 phases

and 0 Amps in 3rd phase ?

If I keep the load on 2 phases only for 8 hours, what are the chances the alternator

will get damaged ?

If I connect a dummy load of lamp banks etc. between 3rd phase & neutral to bring

the load up to 250A, will it save the alternator from damage ?

Regards

__________________
We Are In Current Control !
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#1

Re: 2 Phase Load on 3 Phase Alternator

03/15/2011 3:19 PM

First, I'm curious. I presume that the 250 amp load is really a single phase load (which you will connect between two of the phases). Yeah, it has to be.

Ok, 2nd question--you don't mention the voltage of the load--what is the actual load in kva or kw?

The main concern is the buildup of heat in the windings. Depending on whether the generator winding is wye or delta, you will be drawing the entire load current from one or two windings instead of all three. I'd feel real safe if you're total load is 1/3 of 500 kva. If higher than that, find out the winding arrangement of the generator--with a Y, I'd consider going to 2/3 of 500 kva.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: 2 Phase Load on 3 Phase Alternator

03/15/2011 3:43 PM

I suspect that the 2 phase load is actually expecting a single split phase voltage where the voltages are 180° from each other. If this load requires a real 2 phase voltage than the voltage phase angle will be 90°. This is an ancient form of power distribution that may still exist somewhere but the OP must more clearly specify which type of power is required.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: 2 Phase Load on 3 Phase Alternator

03/15/2011 5:54 PM

For my fellow Americans, people in other parts of the world never had to deal with real "2-phase" power, that which is 90° out. They therefore routinely refer to "2 out of 3 phases" as being "2 phase". We call that single phase here because for us, there is another power system that is (was) really 2 phase power. It's a semantics problem that vexes all international EE forums.

And by the way redfred, phase angles on 3 phase power are 120° out, not 180 , but I know you knew that.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#4
In reply to #3

Re: 2 Phase Load on 3 Phase Alternator

03/15/2011 6:37 PM

We specify "single phase" (L and N) or "3 phase" (U V W[1] (and possibly N)).

The term "2 phase" is not used for mains power distribution.

[1] Some may say R G B, or L1 L2 L3 - but you get the idea.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#7
In reply to #3

Re: 2 Phase Load on 3 Phase Alternator

03/16/2011 9:48 AM

The 180° phase comment was referring to the split phase voltages which are just inversions of the same phase.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Anonymous Poster #1
#5

Re: 2 Phase Load on 3 Phase Alternator

03/15/2011 11:42 PM

As long as the generator winding can carry the rated current i don't see any problem.

Register to Reply
Commentator

Join Date: Mar 2006
Location: Sydney, Australia
Posts: 96
Good Answers: 5
#6

Re: 2 Phase Load on 3 Phase Alternator

03/16/2011 12:14 AM

YES is the answer and monitor the heat on the genset. If it becomes excessive, stop the test.

__________________
Mark Taylor, Senior Technical Advisor, CV Bli Tek, Bali, Indonesia.
Register to Reply
Active Contributor

Join Date: Sep 2008
Location: Mumbai, India
Posts: 14
#8

Re: 2 Phase Load on 3 Phase Alternator

03/16/2011 11:55 AM

Dear Friends,

Thanks for all the replies and sharing of experiences. The answers to all the queries are as follows :

- The set-up is a heat run test on a single phase loco transformer during prototype testing

- The voltage is 415V (fed through a dimmer & step-up transformer to the test job)

- We are using a DG set as the factory has limited grid power and outages are common

- The testing load is actually 130 kVA which is the full load loss of the transformer under test. But the type testing involves 2 hours of 150% loading i.e. 200 kVA ie. approx 280A @ 415V

- The alternator manufacturer confirms that it is safe to load a 500kVA DG set to the extent of 300A on 2 'legs' with no current in one 'leg' for a period of 8 hours

- As a contingency, if the DG trips on Over-Current / Earth Fault / High Temperature we shall switch to grid power with all other factory loads switched off

- Finally, the testing is scheduled on Friday and I will communicate the results to all

Thanks again....and keep posting !

__________________
We Are In Current Control !
Register to Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#9

Re: 2 Phase Load on 3 Phase Alternator

03/17/2011 8:33 PM

I think we are talking of loads that are not symmetrical(unbalanced loading) here and since its a three phase 4 wire,the neutral here will take some value of current which i think is not safe.

__________________
Patrick Whowha
Register to Reply