Star is open,still motor is working

03/17/2011 1:52 PM

we have one one motor having rating:3phase,230/400V+/-10% Delta/star,50HZ,0.50KW,2.96/1.71A,cos phi 0.58.

We run this motor in star connection,but at star end only R & Y phase are shorted,and B is open.But still the motor is running properly without any problem.

Please explain,how it is working.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Star is open,still motor is working

03/17/2011 2:35 PM

A possibility is that where the blue phase is broken the leg to the star point has shorted to earth. Have you done an IR test on the motor? The O/L's should have picked up the imbalance.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Member

Join Date: Mar 2011
Posts: 8
#2
In reply to #1

Re: Star is open,still motor is working

03/17/2011 2:45 PM

Blue phase is not broken,three star wires are coming out.And accordingly to vendors design only, two phase are shorted.So how it is possible,please explain.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Star is open,still motor is working

03/17/2011 2:50 PM

"...without any problem"

That probably should be "without any PERCEIVED problem. if one connection is open, you are single phasing and even though the motor may be turning, you don't have full power available from it.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: Star is open,still motor is working

03/17/2011 3:48 PM

Beats me how it starts

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5
In reply to #4

Re: Star is open,still motor is working

03/17/2011 7:15 PM

My guess; what you thought of first, even with a bad ground path, which provides just enough rotation to get it started moving, then the load is so light that the single phasing once it is already moving provides enough power to keep it moving.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#6

Re: Star is open,still motor is working

03/18/2011 5:43 AM

How do you know the B phase open?

__________________
Anything that can go wrong, will go wrong
Register to Reply
Member

Join Date: Mar 2011
Posts: 8
#10
In reply to #6

Re: Star is open,still motor is working

03/18/2011 5:55 PM

6 wires are coming out,it is installed in a panel.and connected in a above mention way.

Register to Reply
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#7

Re: Star is open,still motor is working

03/18/2011 10:26 AM

I have seen the thing like this also - it is possible with small motors. Power, I believe, is then reckoned not by multiplying by sq root 3 but by sq root 2.

Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#8
In reply to #7

Re: Star is open,still motor is working

03/18/2011 11:16 AM

But things are going... in not the way we know. Why?

__________________
Anything that can go wrong, will go wrong
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#9
In reply to #8

Re: Star is open,still motor is working

03/18/2011 12:02 PM

Line voltage differs from phase voltage. The former produces different emf's in both remaining windings of the motor (that is, maybe better to say, the source, a generator , or a transformer produces) while the latter creates the same emf in the both.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#11

Re: Star is open,still motor is working

03/18/2011 8:32 PM

Are you using Star-Delta starting perhaps? If so, then it could be that when you start it, there is a partial path but when running you end up losing one set of windings, but it is already spinning at that point, in which case refer to the above.

You really are not being very clear about what you have and what is being used to start it etc. Any chance you have a drawing you can post?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 11 comments
Copy to Clipboard

Users who posted comments:

electrahul (2); hien.nguyenquoc (2); JRaef (3); TonyS (2); Yuri B. (2)