What Would Have Happened?

03/19/2011 3:36 PM

Here's one to ponder on.

A few years back we had a fault on a 33/11KV 20MVA transformer. Buchholz surge, it was due to low oil level. It was the middle of a freezing night so it was decided to leave it until daylight and just close the bus-section to get the plant up and running. Walking out of the switchyard I hit one of the liquid NER tanks with an 18" spanner out of shear frustration. That didn't sound right thinks I, we had a ladder with us so I climbed up and opened the cover. Oh S**T was my reaction. The tank was bone dry, the electrode was so corroded it had collapsed. Effectively we had no earth on that transformer. We had 3 more units but at 3AM I wasn't looking in to them.

The question is what would have happened if we had a phase-earth fault on the 11KV system?

I've had all sorts of lurid ideas, none of them very pretty!
Checking the other units didn't look very good, all had to be taken out of service in turn for major repairs. It wasn't poor maintenance, it was pure neglect!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#1

Re: What Would Have Happened?

03/20/2011 3:46 AM

No earth was left on both circuits - neither on 33kV nor on 11kV ?

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: What Would Have Happened?

03/20/2011 6:07 AM

11KV side only. The 33KV side was the responsibility of the supply company.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#3
In reply to #2

Re: What Would Have Happened?

03/20/2011 6:30 AM

Frightening picture, of course, but hopefully the potential on the low side transformer construction would be earthed through the high side. The consumers of the 11kV would also soon have sensed voltage drops and attended. I believe there was more possibility of fire than el. shocked people and/or damaged equipment other than that system itself.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: What Would Have Happened?

03/20/2011 8:17 AM

It was our own private system covering a large site with a few subsidiary supplies to leased sites.

My thoughts were that if one phase grounded, the other two's potential to earth would be raised and potentially flash over.

__________________
The reports of my death are greatly exaggerated.