Open Circuit Phase on STAR Transformer

03/21/2011 2:32 AM

hi guys, if you have a 415V 3 phase STAR transformer with a balanced load, you get 240V between phase and neutral and 415V between phases. If you have unbalanced loads across the 3 phases, you will get a voltage induced on the neutral point and hence your phase voltages will not be equal. This is because the vector sum of currents at the neutral point is no longer zero. Can someone confirm this: If you open circuit one of the phases, does the phase voltage between the two active phases become 415V/2 = 207.5V and no voltage is induced on the neutral point?

__________________
Electrical Engineer
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Open Circuit Phase on STAR Transformer

03/21/2011 11:07 AM

Where are you referencing voltage?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Commentator

Join Date: Jul 2010
Posts: 92
Good Answers: 1
#3
In reply to #1

Re: Open Circuit Phase on STAR Transformer

03/21/2011 6:27 PM

to the neutral point of the STAR connection on the load side.

__________________
Electrical Engineer
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#2

Re: Open Circuit Phase on STAR Transformer

03/21/2011 11:19 AM

If you mean by "Star transformer" the secondary windings of a transformer to which load is connected, then the voltage does not depend on the load, as well as it does not depend on the load balance (so long as the power of the load does not ecxeed much the power of the transformer, if exceeds, then voltage will "drop").

Register to Reply
Commentator

Join Date: Jul 2010
Posts: 92
Good Answers: 1
#4
In reply to #2

Re: Open Circuit Phase on STAR Transformer

03/21/2011 6:30 PM

What if one phase is not connected and left open circuited? Doesn't that mean the neutral point now has a voltage present, because the vector sum of voltages at this point is no longer zero? Between phases you would still see 415V, but if you were measuring from phase to neutral, then you would see <230V? (not sure what it would be)

__________________
Electrical Engineer
Register to Reply
Power-User

Join Date: Oct 2008
Location: Thousand Islands, Ontario, Canada
Posts: 187
Good Answers: 9
#5

Re: Open Circuit Phase on STAR Transformer

03/22/2011 12:52 AM

No, you get 240V, even if you open two phases. So long as you don't exceed the individual phase rating of the transformer. If you have a 3KW transformer and draw 1KW on an individual phase, you'll still be getting near 240V line to neutral.

Register to Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#6

Re: Open Circuit Phase on STAR Transformer

03/22/2011 1:29 AM

Hi

Imballance on Phases, I would be first having a look at the bonding of the main neutral and earth, if this bonding is not effective you will end up with a neutral floating above earth, CHECK THIS OUT FIRST!

Dont get to technical about it all, check the basic's first.

Best Regards

Joe

Register to Reply
Commentator

Join Date: Jul 2010
Posts: 92
Good Answers: 1
#7
In reply to #6

Re: Open Circuit Phase on STAR Transformer

03/22/2011 1:45 AM

this is what I thought, I would like to mention that in this case, I'm assuming a floating neutral. If the neutral weren't floating, you would have higher voltages distributed across phases. How do you have 240V across each phase with an open circuited 3rd phase, if the net result of voltages is no longer 0 at the neutral point?

__________________
Electrical Engineer
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#8
In reply to #7

Re: Open Circuit Phase on STAR Transformer

03/22/2011 8:15 AM

Your Transformer 2ndary is start connected, and Phase to neutral = 240V while Phase to phase = 415V.

Whether the Neutral is grounded or not, and whether one of the phases is not used on the load, the voltages remain the same: i.e. 240V between phase & Neutral and 415 v between phases. The Neutral is not Floating here. the terminology is not usefull in this context.

If your loading circuits are using equipments for 240V rating, and you connect them between a phase and the neutral at the beginning, and suddenly, you disconnect the Neutral from the transformer Neutral but kept the loading circuits as they are, THEN your Loadside Neutral becomes Floating since the equipment that are connected between P & N will become between P & P (P1 & P2 or P2&P3 etc), and since they are not of the same ratings, the artificial resulting neutral will be floating, such that the voltages present at the different equipments will no longer be 240V but somewhere between 0 (not exactly) and the 415 V (also not exactly). Meaning that on one line P to P, some will have less than 240V and some will have higher up to near 415. All depends on the impedence of each connected item.

A complete explanation will take more .... but I hope this will be enough for now.

Register to Reply