hi guys,
if you have a 415V 3 phase STAR transformer with a balanced load, you get 240V between phase and neutral and 415V between phases.
If you have unbalanced loads across the 3 phases, you will get a voltage induced on the neutral point and hence your phase voltages will not be equal. This is because the vector sum of currents at the neutral point is no longer zero.
Can someone confirm this:
If you open circuit one of the phases, does the phase voltage between the two active phases become 415V/2 = 207.5V and no voltage is induced on the neutral point?