Anonymous Poster #1

Transformer Adaptation

03/25/2011 3:41 AM

Dear all, Good day. Just wondering if it is technically possible (excluding the cost) to replace a 155MVA, 11.5kV/132kV generator step-up transformer with a 420MVA, 18kV/230kV spare unit transformer? For the 155MVA unit, the winding ratio would be 1:11.478 while for the 420MVA unit, the winding ratio would be 1:12.778. Is partial rewinding possible in this case? Appreciate if there is any suggestion (best with a rough costing) to adapt the 420MVA unit for the plant operation. Also, do we need to take consideration of the coil & copper winding sizing since the original design was meant for 18kV/230kV? I assume that the core & copper loss would be lesser since we are using a lower rating for the voltage (11.5kV)? Any other factors that I should put into consideration in this case? Please advice. Appreciate for all comments and suggestion. Thank you !

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Transformer Adaptation

03/25/2011 7:47 PM

Unless you are in the transformer design and rewind business I would suggest that you get the proper transformer. There's more to this than simply adding or removing a few coils of copper.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#2

Re: Transformer Adaptation

03/25/2011 11:24 PM

You can replace with the spare one. Use series reactors to manage the voltage differential to an acceptable value. The series reactors will additionally limit the short circuit current and are extensively used.

__________________
Knowledge sharing is a WIN-WIN situation
Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: Transformer Adaptation

03/26/2011 6:02 PM

Although I agree that series reactors can be used to limit short limit currents, please explain how a passive series reactor will "...manage the voltage differential..." since the desired voltage drop will vary as the load through it and the stiffness of the system to which it is attached. A better(?) solution would be to lower the output voltage of the generator to 10.33kV so that the high-side voltage of the replacement transformer remains at 132kV. Of course this ignores the problems of fitting a 420MVA transformer into the space previously occupied by the 115MVA one, the possible impedance differences between the transformers and its effect on system voltage regulation, as well as the potential derating of the generator due to its inability to reach full load current at the lower maximum voltage along with the required retuning of the Automatic Voltage Regulator system. There's more to this question than meets the eye.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#4
In reply to #3

Re: Transformer Adaptation

03/27/2011 12:04 AM

I said "series reactors are extensively used" and if so load variations occor in each and every case, still the systems are manageable.

As for the OP, adjustment of the speed droop of governer will keep the machine steady, while for you the relation of induced EMF per coil is

(weber flux pole * P/60) X (120 * f / P)

and cannot be altered as desired.

__________________
Knowledge sharing is a WIN-WIN situation
Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5
In reply to #4

Re: Transformer Adaptation

03/27/2011 6:16 PM

Please provide an actual example of your proposed series reactor solution. Using random cut and paste factoids only serves to obfuscate not enlighten, the resultant lack of knowledge transfer is not a win-win.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#6
In reply to #5

Re: Transformer Adaptation

03/28/2011 4:26 PM

Dear Ram you are at liberty to start a new thread, as for this space it is the domain of OP and all responses should be relavant to the OP's concerns.

__________________
Knowledge sharing is a WIN-WIN situation
Reply