Dear All,
I am working at Combine cycle plant. we are facing quite
different problem in the boiler feed pump speed control unit/scoop
control. We observed in abnormality in IP Drum feed flow path. We have
torishima make feed pump with hydraulic coupling of voith make.
As 1 year before scoop and other parameters were as under :
We have 2X100 % CV for IP feed Water Flow and 1X30 % CV.
now in 2009 the 100 % CV opening was 52%
feed flow : 11.6 kg/s
DP across CV : 10.9 barg
IP Feedwater Pressure : 46.2 barg
IP Drum level set point : 0.0 mm
Drum pressure : 29 bar
Scoop Position : 64 %
Pump RPM : 2847
RPM Set Point : 2843
power o/p : 391 MW
Now current condition is quite different. HP Drum and LP drum is
same as 1 year before. Abnormality observed and Speed control
fluctuation observed in IP path only.
at present parameter observation are as under :
100 % CV opening : 51.4%
DP across CV : 13.4 barg
IP feed Water P : 49.2 barg
Drum level set point : 0.0 mm
scoop positin : 71 % to 100 % (100 % mostly)
Pump RPM : 2890
RPM set point : 2880
Power O/p : 380 MW
Grid Frequency : 49.65 to 49.90 (Not Fluctuate frequently)
Rated motor RPM : 2980
Control action checked in DCS logic it is found normal.
So what can be the problem why scoop goes to 100 % frequently even load fluctuation is not there. Load is constant but scoop is changing from 71 to 100% and stuck at 100 % mostly except major load variation.
Good Answers:
"Almost" Good Answers: