About Current Transformers

04/01/2011 8:46 AM

Dear sir, i wanted accurate voltage as output from current transformer for that i have connected one resistor parallel to the out put of CT, then i getting the voltage but not accurately. so please help and tell me how to get the good results. thanking you sir

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Sep 2008
Location: Jakarta, Indonesia
Posts: 104
#1

Re: About Current Transformers

04/01/2011 1:45 PM

Accurate voltage will not be you got from CT that you give resistor,

because your CT is in series with Load. and then between Source (220V or 380V or 11kV or 20kV) to Load you give CT.then you put resistor in there. so your voltage is change following the change of your load.

better you use VT in paralel with your source to get stable voltage.

thanks & warm regard

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: About Current Transformers

04/01/2011 5:24 PM

As far as I'm aware you should get a linier voltage range. I've used this method for under load detection for belt driven fan drives.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 134
Good Answers: 11
#3

Re: About Current Transformers

04/03/2011 1:55 PM

Your load resistor probably has too high a resistance. Try it with a load resistor of much less than 1 ohm.

OR put your mutimeter on 10 or 20 amp AC and connect directly to the current transformer output. CAUTION: Verify that you multimeter is working correctly before doing this. If the multimeter has an open fuse or is not working correctly, you may destroy both the multimeter and the current transformer.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: About Current Transformers

04/03/2011 3:58 PM

Are you exceeding the burden rating of your CT or driving the CT outside its linear operating zones?

Are you wanting a fixed voltage but it is changing as your current changes?

What are you using the voltage for?

Can you please supply more information regarding your application.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: About Current Transformers

04/06/2011 12:06 PM

I assume that you are measuring the CT Secondary Voltage with a Voltmeter. If so, voltmeters have a very high Ohmic burden. If this burden is more than the CT Rated Burden, then definitely the CT accuracy will be affected.

Register to Reply
Register to Reply 5 comments
Copy to Clipboard

Users who posted comments:

Carl Pugh (1); elect-ok (1); electricalexpert65 (1); jack of all trades (1); TonyS (1)