Transformer Initial Inrush

04/03/2011 4:36 PM

Dear CR4 Members

Please tell me if the initial inrush to a brand new transformer would be greater than say a transformer that has been soaked or in service and then re-energised.

I'm working in Ireland and i switched in a 2.5MVA transformer that was protected by a SIEMENS 7UM611 Relay.

The problem is that Networks Protection kept tripping on inrush and causing my relay is issue a undervoltage trip.

This is a 20kV network that is feeding a group of Wind Turbines.

I eventually managed to close the circuit by switching on in stages but if there is ever a power failure then my protection will issue a trip and only reclose after 20 minutes of uninterupted restored supply.

I'm worried that the Networks Protection will operate again or will the inrush be less.

The Wind Turbines are in a remote location and having to travel to reclose manually every time there's an outage would be madness.

Thanks for your time

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Transformer Initial Inrush

04/03/2011 4:58 PM

How many transformers / inductive loads are down stream of the primary TX?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Member

Join Date: Mar 2011
Posts: 8
#2
In reply to #1

Re: Transformer Initial Inrush

04/03/2011 5:10 PM

TonyS

There are two 2.5MVA Primary Transformers each stepped down to 660V connected to to Inverters connected to 2.4MVA DC Turtine Generators.

Register to Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#3

Re: Transformer Initial Inrush

04/03/2011 9:45 PM

Nothing of the sort I've read or heard about and there's no logic supporting it. Check the accepted connection sequence of the inverters. Also possible is their internal over-voltage protection triggered at -random time- C/T connection, or not yet run-in bulk capacitors that caused the inrush overcurrent. Is the problem now reproducible?

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Commentator

Join Date: Feb 2011
Location: Dubai, UAE
Posts: 63
Good Answers: 7
#4

Re: Transformer Initial Inrush

04/03/2011 11:08 PM

Magnetic inrush will be the same in all cases.

Problem might be due to inadequate capacity elements like cables causing excessive voltage drop at inrush and the relay trips.

Since you have demonstrated that switching in stages overcomes the deficiency most easy solution would be to incorporate time delays so that in case of automatic restoration the time grading keeps the system stable.

Besides the protection relay time grading can also be accomplished by incorporating timers in the closing coil control circuits of the CB's.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#7
In reply to #4

Re: Transformer Initial Inrush

04/05/2011 7:13 PM

Sorry AA, the maximum inrush current does vary according where in the sine wave the voltage is when it is applied. It is highest when it is being energized from the HV side at the instant the supply voltage passes through zero. Energizing a core-form transformer from the LV side may result in inrush currents approaching twice as high. The per unit inrush current to a shell-form transformer is approximately the same on the HV or LV side.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Power-User

Join Date: Jun 2010
Location: Canada
Posts: 139
Good Answers: 6
#5

Re: Transformer Initial Inrush

04/04/2011 11:04 AM

YES, . . you will get different inrush - with different transformers, especially when comparing new and efficient transformers with the older ones and less efficient ones. New transformers will have a high-grade, low-loss core that has a pronounced knee-point what promotes inrush. Also, new and highly efficient transformers have lower winding resistances - that further promote inrush, once the core is saturated. You will just have to re-set your relays, . . or to use better relays that recognise inrush . . . . Oleh

Register to Reply
Anonymous Poster #1
#6
In reply to #5

Re: Transformer Initial Inrush

04/04/2011 11:48 AM

We're talking about the same transformer inrush current differences from when it's brand new and when been in service. Can you support any theory about it?

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#8

Re: Transformer Initial Inrush

04/05/2011 7:34 PM

The initial inrush current varies according to when in the cycle it is energized.

More info is required to know what is causing the OC relay to operate, but my guess is that your windfarm consists of a number induction generators radially connected via buried three phase cables all leading to your transformer then out to the grid. If this is true then you need to account for the inrush current for the generators especially if the turbines are not operating near their synchronous speed when they are energized. I suspect this is the case because you have found that if you energize the turbines sequentially the relay doesn't operate. Sounds like a microprocessor programmed to sequentially apply the turbines might save you from running out there every time the wind starts blowing fast enough.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Member

Join Date: Mar 2011
Posts: 8
#9
In reply to #8

Re: Transformer Initial Inrush

04/06/2011 4:49 AM

Thanks for your comments.

The wind turbine generators are DC and the Inverters do the Synch. Each turbine has its own transformer.

the turbines only turn if there is supply or else they mechanically lock out until supply returns.

Im thinking that the capasitor banks inside the inverters caused the inrush to be greater than normal because they had never been energised.

Also i think that the Networks protection was too tight.

Ill be returning in a few weeks to simulate a loss of grid supply to see if the system can restart on its own.

cheers