Dear CR4 Members
Please tell me if the initial inrush to a brand new transformer would be greater than say a transformer that has been soaked or in service and then re-energised.
I'm working in Ireland and i switched in a 2.5MVA transformer that was protected by a SIEMENS 7UM611 Relay.
The problem is that Networks Protection kept tripping on inrush and causing my relay is issue a undervoltage trip.
This is a 20kV network that is feeding a group of Wind Turbines.
I eventually managed to close the circuit by switching on in stages but if there is ever a power failure then my protection will issue a trip and only reclose after 20 minutes of uninterupted restored supply.
I'm worried that the Networks Protection will operate again or will the inrush be less.
The Wind Turbines are in a remote location and having to travel to reclose manually every time there's an outage would be madness.
Thanks for your time