Minimum Period to Record Reading for VFD

04/06/2011 10:28 PM

Supply fan 3 phase, ,AC induction motor, 22Kw ,400v ,1450 rpm, 50hz .When checked with fluke power analyzer model 435 the readings were 15kw,26amp ,50 hz. 900 rpm checked by tachometer. A demo inverter of 45 kw rating was installed on the existing induction motor. THe reading recorded on the primary side of the inverter after 1 mnt were 13.7kw, 20amps, 900rpm and the saving was calculated (on the basis of 1mnt)..My question is that what should be the minimum period( 24 hrs, one week ) for recording the correct readings so that actual saving can be calculated for VFD run motor vrs standard run AC motor. For actual saving calculations purpose reading of secondary side of inverter is to be recorded or primary side.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: minimum period to record reading for vfd

04/06/2011 11:31 PM

1 year.

Seriously, the only way to truly know your comparative savings in an HVAC system is to record use throughout a complete temperature-year. Everything less than that is going to be an extrapolation, so any time interval you chose needs to be weighed against what it means when temperatures vary and how important total accuracy is. because the longer your VFD driven system runs WITHOUT reducing the speed, the more LOSSES you will incur, which will offset the savings.

I'm not saying that VFDs don't save energy, but looking at the savings in one day, one week or even one month is relatively meaningless unless you have a very even temperature throughout the year. And if you do, and your system CAN run at a reduced speed, then someone over-designed your system..

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 4)
Active Contributor

Join Date: Mar 2009
Location: Vancouver, WA USA
Posts: 14
#3
In reply to #1

Re: minimum period to record reading for vfd

04/08/2011 8:46 AM

If you are talking HVAC, even this won't give you an accurate picture of your savings. You would have to factor in weather for the base year energy consumption and the current years' consumption.

Now, if you are talking a fan that runs under a steady load for continuous ventilation, boiler fan, etc, you could calculate the power based on you meter readings with and without the VSD. Take the difference and multiply times the annual run hours and you have annual energy savings.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#5
In reply to #1

Re: minimum period to record reading for vfd

04/08/2011 5:36 PM

First part I agree with. The best way to get an actual pay back is to evaluate a full years worth of run time. You could take the annual power costs from the previous year and calculate the savings in an ROI form for a payback basis but the best way is to compare both annual utility costs.

As far as the system over sized, not true. Many systems until the late 90's were designed as VAV (variable air volume) systems that would run full speed on the fans until the different zones in the buildings were satisfied. Upon satisfaction the air dampers for that zone would close and force the air into a "By Pass" and dump into a return air plenum or shaft which would then be removed from the building Via a relief fan.

Today when the dampers close the by passes have be closed (so you do not waste conditioned air) which allows the static pressure in the duct to build. That higher pressure is then sent to the VFD (VSD) via a transducer to tell the motor to slow down since you now have enough static pressure in the duct work to run the system.

Same is used in water heating systems today, the slower you can move the water through the fan coils or floor the more heat the piping can give up to the space. A 3-way or bypass valve should be used in reheat or heat systems so that once the zones become satisfied the bypass valve (3-way) opens and sends the not needed hot water back to the boiler or source raising the temperature in the supply vessel allowing it to turn off an not waste any more therms.

So they were not over designed they were designed for the times.

__________________
To be or not to be........ok that's a trick question.
Register to Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#2

Re: Minimum Period to Record Reading for VFD

04/08/2011 4:03 AM

Hi I am not sure about the question that you are asking, please correct me if I am wrong. You had a 3 phase motor connected via Dol, then you connected a VSD to the same fan, am I correct so far?

When you also measure the current through a VSD things change, but I don't know about you Fluke Power Analyzer.

The problem is, that i can see is that you are measuring the line amps and line voltage to the VSD this does not have a linear reference to the power consumed by the VSD, this is because of the way the VSD operates in prince-able.

VS-D's are a bit like switch-mode power supplies they create harmonic frequency's, which can be bad for the power supply. This is an area that I am not so familiar with, but have accepted, this is not my strength!

VS-D's Have used what we call an energy saving mode, but with a fan, and not completely understanding your application, I don't know if this could be applied.

The thing about it is You have a fan, but you want to reduce the energy that this fan uses, why not put some power factor correction on the fan motor, because the fan will will only draw the current required to move the air required.

There would be little or no saving by installing a VSD to operate at a constant speed, but if you want to vary the speed, go for it mate.

Best Regard's

Joe

Register to Reply
Anonymous Poster #1
#4
In reply to #2

Re: Minimum Period to Record Reading for VFD

04/08/2011 1:57 PM

"...prince-able"

= principle.

Just being a word nazi, sorry.

Register to Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#6
In reply to #4

Re: Minimum Period to Record Reading for VFD

04/08/2011 5:57 PM

Spelling is not one of my strenghts either

Cheers

Joe

Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Joe Sparky (2); JRaef (1); MLHemmer (1); Stedou73ish (1)