04/08/2011 11:30 AM

Hi all,

Today the consultant came to me with the catalog of severals RCCB and RCBO. I noted there were 02 kinds of RCBO with 32A/30mA, but the short circuit capacity is different 4.5kA and 6kA.

1. Which one I should choose. He suggested me to choose the one with 6kA SC current. I want to know if it is the breaking current or SC withstanding capacity? From what I know, RCCB or RCBO do not have SC protection capability. Should I choose the one with 6kA SC current?

2. Is RCD same type of equipment with the above?

3. From what I learn from the above, if I have to choose breakers (let's say MCB), I have to consider two things (SC breaking current and SC withstanding current)? What if the divide has only one parameter?

__________________
Anything that can go wrong, will go wrong
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Short Circuit Currents of RCCB & RCBO

04/08/2011 1:38 PM

You are using the terms RCCB and RCBO, which implies that you already know the difference between them. RCCB does not have overcurrent capacity, while RCBO has.

Please check out this link : http://en.wikipedia.org/wiki/Residual-current_device

The choice of what short-circuit level you need should be based on a good study. In case you can't find this figure, you need to pick the best that is available.

Good luck.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Short Circuit Currents of RCCB & RCBO

04/08/2011 3:14 PM

This begs the question, do your employers allow you to specify purchasing requirements?

From some of your recent posts on the board you don't seem able to make a decision.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#4
In reply to #2

Re: Short Circuit Currents of RCCB & RCBO

04/09/2011 12:10 AM

Thank you, TonyS.

__________________
Anything that can go wrong, will go wrong
Register to Reply
Active Contributor

Join Date: Aug 2008
Location: New York
Posts: 16
#3

Re: Short Circuit Currents of RCCB & RCBO

04/08/2011 11:49 PM

Before you attempt to make any decisions, you should perform good short-circuit study in your system and them check the products (manufacturer and other info available); only them you will know what do you really need. If you make your decisions only based on the consultant, you might make a big mistake. Usually, consultants offer what will bring them more profit or easier work!!!!!! Well, with today's economy, who wouldn't do that?

__________________
...
Register to Reply
2
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Short Circuit Currents of RCCB & RCBO

04/09/2011 8:35 AM

Please note that MCBs (as well as RCBOs) belong to Utilisation Category 'A' - which means that they do not have an Icw (Short Time Withstand) Rating. They cannot tolerate carrying short circuit current. Thts why they do not have a delay setting in their short circuit protective releases, which are instantaneus.

Between 4.5kA & 6kA- you have to select the breaker whose breaking capacity is more than the fault level at the point of installation. If the fault level is less than 4.5kA, then there is no point in going for a 6kA MCB. May be the consultnt wants tio be safe as he may not be aware of the fault level at your installtion. So, he suggests 6kA.

The 4.5kA or 6kA mentiones is the short circuit breaking capacity ad definitely NOT the short time withstand current rating.

And, RCCB does not have SCprotction capability. Only an RCBO has. An RCCB must always be bae up by a SCPD (Short Circut Protective Device).

An RCD is Residual Current Device, a device also knon as ELCB or RCCB.

For MCBs you need not consider SC withstand current as they would not have a rating for the same.

Register to Reply Good Answer (Score 2)
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#6
In reply to #5

Re: Short Circuit Currents of RCCB & RCBO

04/09/2011 10:36 PM

"Between 4.5kA & 6kA- you have to select the breaker whose breaking capacity is more than the fault level at the point of installation. If the fault level is less than 4.5kA, then there is no point in going for a 6kA MCB. May be the consultnt wants tio be safe as he may not be aware of the fault level at your installtion. So, he suggests 6kA". I think this is a good piece of work.

But, it is not correct when you said "RCCB does not have SCprotction capability. Only an RCBO has". RCBO has over current protection only.

Moreover, is there any confusion between your Short circuit and over current protection? I think we just can apply delay for over current protection only. It is too dangerous when we intend to delay in short circuit protection.

As my conclusion, the SCs rated on those RCCB and RCBO are withstanding capability. The bigger they are, the better they can withstand.

__________________
Anything that can go wrong, will go wrong
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#7
In reply to #6

Re: Short Circuit Currents of RCCB & RCBO

04/10/2011 12:01 AM

hien.nguyenquoc,

You have some misconceptions which may prove lethal. Please check out elsewhere, if you do not believe EE65 and me and others here.

1. MCBs, RCCBs and RCBOs DO NOT have SC withstand capacity, they are current limiting devices. Yes, the big devices have withstand capacity, Icw. See Air Circuit Breakers.

2. RCCBs DO NOT have the capacity to break short-circuit currents. They need other SCPDs in addition, as mentioned by EE65. When the two devices are combined into one, it is called an RCBO.

3. "Overcurrent" is a generic name given to overloads and short-circuits. An RCCB has no overcurrent protection at all, it is only for earth leakage protection.

The devices you are referring to are to protect people in a home or an office. Please be very careful.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#9
In reply to #7

Re: Short Circuit Currents of RCCB & RCBO

04/10/2011 12:36 AM

1. If so, what does the SC rating on the RCCB and RCBO means? Does it only imply that these equipments should be used if the pre-calculated SC in the system is less than that?

2. RCCBs DO NOT have the capacity to break short-circuit currents. I do not have any doubt in this. I am having in my hand the catalog (very famous manufacturer in EU, sorry I will not show the name not to damage that brand name) which written that: "RCBO - Against overcurrent and insulation fault". So I think that it will be much better and safer if they write "RCBO-Against Short circuit and insulation fault". This is the point making us confused.

3. Overcurrent and SC cannot be used interchangeable. But in the EE65 implied that we can delay the SC interrupting time? Is that correct? I think it is unsafe except for the case of overcurrent.

That is why I am struggling to find the hidden truths in these things. That is why I am questioning you until it is very very clear. I will allow them to use it.

__________________
Anything that can go wrong, will go wrong
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#11
In reply to #9

Re: Short Circuit Currents of RCCB & RCBO

04/10/2011 1:18 AM

RCCBs DO NOT have the capacity to break short-circuit currents. I do not have any doubt in this. I am having in my hand the catalog (very famous manufacturer in EU, sorry I will not show the name not to damage that brand name) which written that: "RCBO - Against overcurrent and insulation fault". So I think that it will be much better and safer if they write "RCBO-Against Short circuit and insulation fault". This is the point making us confused

i already said "Overcurrent" includes overload and short-circuit. So, nothing wrong with what the manufacturer says. And he is saying that about RCBO. Not RCCB.

Overcurrent and SC cannot be used interchangeable. But in the EE65 implied that we can delay the SC interrupting time? Is that correct? I think it is unsafe except for the case of overcurrent.

SC is a subset of overcurrent. Of course we can delay the tripping of an upstream circuit breaker to allow a downstream one to clear the short-circuit. EE65 is quite correct. The whole system of time-based discrimination in distribution systems is based on this. But remember, these generally are ACBs, which have the ability to withstand the short-circuit current for some specific time, usually 1 second. Check the web for discrimination systems, there is a lot of information out there.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
2
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#8
In reply to #6

Re: Short Circuit Currents of RCCB & RCBO

04/10/2011 12:25 AM

I personally feel that you need a refresher course in Protection & Co-ordination.

I repeat - I repeat - that RCCB does not have Short Circuit Protection. In any RCCB name plate, only the rated current and sensitivity are mentioned (e.g.) 40A, 30mA. If an RCCB has got a SC Proetection & Breaking Capacity, why it is not mentioned in its name plate? Can you show me an RCCB which has got a SC Protection & Breaking Capacity?

Though going by the Standards, there is no difference, whatsoever, between Overcurrent & Short Circuit - in an MCB, overcurrent protection is normally provided by a bi-metallic element and the short circuit protection is provided by a magnetic trip unit.

And, you are very incorrect in stating that it is too dangerous to delay short circuit protection. In fact, the very principle of Time Discrimination is based on delaying the tripping times of upstream SC Protective Devices, with respect to downstream devices. If there is no delay possible in SC Protection, then how will you avoid the incoming breaker tripping (and thus causing a total black-out) for an SC fault in a downstrm feeder? Please attend as soon as possible a course on Protective Device Co-ordination.

And, again, an RCCB would not have an SC Rating. The SC Rating marked on an RCBO is called it Short Circuit Breaking Capacity (and, definitely NOT its Short Circuit Withstand Capability). If, as you say, it is the Withstand Capability, then why the withstand time is not mentioned? Any with stand should also have a withstand time duration. Isn't it?

Register to Reply Good Answer (Score 2)
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#10
In reply to #8

Re: Short Circuit Currents of RCCB & RCBO

04/10/2011 12:46 AM

EE65:

Thank you for correcting me. I got a mistake in interpreting RCCB and RCBO and am really sorry for this confusion.

RCCB does not have SC protection.

RCBO is a combination of RCCB and SCPD.

Normally, I use one RCCB combined with MCB to provide full protection for the downstream circuit. The problem looks better now and I think I will go on with that.

__________________
Anything that can go wrong, will go wrong
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#12
In reply to #8

Re: Short Circuit Currents of RCCB & RCBO

04/10/2011 5:59 AM

Both your 'almost' GAs are good, so i have added my GAs. i do hope that the OP will do some more study and learn more about switchgear.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 6)
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#13
In reply to #8

Re: Short Circuit Currents of RCCB & RCBO

04/11/2011 11:42 PM

EE65,

Could I change the topic a bit more to the breakers?

So, to have a good discrimination in power system, we need to choose the correct breakers. As you mentioned the SC capacity should have a withstand time, when refer to this below photo, I could not find it.

This is leading me to the below idea.

We will select the downstream breakers which have a little faster tripping time. But the breaker itself is not enough. We need to check its serial number, then refer to the catalog or manual to check out the protection curve/SC withstand time. The lower curve will show the downstream breaker, the higher curve will show the upstream breakers? Is my understanding same as yours?

__________________
Anything that can go wrong, will go wrong
Register to Reply
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#14
In reply to #13

Re: Short Circuit Currents of RCCB & RCBO

04/12/2011 5:10 PM

Depending on the regulations where you are based, an RCCB may or may not need to have it's short-circuit capacity printed on the case but regardless of this it will very definitely have a short-circuit capacity that the manufacturer has had it tested to.

The trick here is to download for yourself a copy of the manufacturer's datasheet or technical catalogue, and have a good look in there. In the case of the MG brand in your photo, it should be child's play to find this data.

__________________
paulusgnome
Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

electricalexpert65 (2); hien.nguyenquoc (5); kvsridhar (4); Paulusgnome (1); Reynal74 (1); TonyS (1)

Previous in Forum: Design Of Input & Output Choke For VFD   Next in Forum: 555 Monostable Circuit Puzzle

Advertisement