Utility main switch re-closure

04/09/2007 9:29 AM

Am working on a project that we need to parallel reciprocating generator sets (10.5kV) with grid (220KV), the local grid company requires main switch single phase reclosure within 0.5s. Our concern is whether or not the surge from single phase reclosure will damage certain alternator parts like rotating rectifier?

Some people think the single phase reclosure shall be no problem because single phase will ensure the gensets are in sync with grid when reclosing. Others think it will damage the rectifier because the unbalance load from single phase trip and reclose. Would appreciate if anyone has experience in this area to give me some advices!

Thks.

Register to Reply
Pathfinder Tags: Reclosure
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Popular Science - Weaponology - New Member

Join Date: Feb 2006
Posts: 962
#1

Re: Utility main switch re-closure

04/09/2007 9:43 AM

10.5Kv to 220KV supply? Think about it! The higher voltage will melt your gen sets and some.

__________________
There's them that knows and them that just thinks they know, whitch are you? Stir the pot and see what rises up. I have catalytic properties I get a reaction going.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Utility main switch re-closure

04/09/2007 3:41 PM

Are you trying to parallel connect two (or more) 10.5kV single phase generators to the local single phase 220kV supply (using, I am assuming, a 10.5-220kV step up transformer) using a single recloser?

What is the supply current?

I am assuming you are looking at a recloser that is designed for this (not all of them are).

__________________
jack of all trades
Register to Reply
Active Contributor

Join Date: Apr 2007
Posts: 16
#3
In reply to #2

Re: Utility main switch re-closure

04/10/2007 9:32 AM

jack, yes, we are connecting fifteen 10.5KV gensets to a 220KV grid via step up transformer, the 220kV main switch to the transmission line will attempt to reclose once for any line problem, if this reclosure affort fails then the switch will stay tripped... this is the requirement from local grid.

We are concerned this one time reclosure (within 0.5s) will damage the alternator rectifier, however, such single line re-closure is quite commonly required by grid company worldwide... so we doubt whether truely it can damage the alternator.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4
In reply to #3

Re: Utility main switch re-closure

04/10/2007 4:37 PM

I have not had any experience trying to grid tie this many generators (of this high voltage) to the network. Previously I have done it using a Siemens feeder management relay controlling a vacuum interrupter switch on the HV side (before the transformer), but that was as a fully protected and controlled substation designed for parallel and island mode operation, and the generators were only 415V.

I think the generator company you got the generators from would be the best place to start asking these questions, and also run it past the recloser manufacturer. They should have the experience to answer these sort of special application questions.

AtLeast that is what I would do.

__________________
jack of all trades
Register to Reply
Anonymous Poster
#5

Re: Utility main switch re-closure

04/11/2007 11:22 AM

Jack gives proper advice the entire gen system regulator speed control all of it is at risk if the units are not designed for the application re closures can be real blast , figuratively and literally!

Jon