Sizing Switchgear According to SC Current

04/19/2011 12:44 AM

One 22/0.4kV 2000kVA Transformer fed by 110/22kV 64 kVA substation. The distance is about 300 meters from the HV substation. Power is delivered from HV substation by aboveground ASCR 250mm2 cable.

From the connection point, power supplied to this LV transformer by underground 150mm2 copper cable.

To estimate the short circuit current on the primary side of 22/0.4kV transformer, which information do we need to collect?

Can we utilise the SC current available on 22kV provided by Power Company?

__________________
Anything that can go wrong, will go wrong
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Mar 2011
Posts: 13
Good Answers: 1
#1

Re: Sizing switchgear according to SC current

04/19/2011 3:30 AM

The power company should be able to give you the source impedance of their network feeder to your facility (i.e. at the point of common coupling), which I presume in your case is the 22kV side of your transformer.

You can use this source impedance to calculate all the short circuit levels in your system, including at the 22kV side of your transformer. Often they'll give you the SC capability of the source in MVA, but you can easily convert that to an impedance value.

Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#2
In reply to #1

Re: Sizing switchgear according to SC current

04/19/2011 3:56 AM

If it is difficult to ask them for the source impedance, may I change the question by asking them the impedance of transformer and ASCR line?

Sorry, I got one mistake with 110/22kV transformer. Its capacity shall be 64MVA.

__________________
Anything that can go wrong, will go wrong
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3
In reply to #2

Re: Sizing switchgear according to SC current

04/19/2011 6:51 AM

You must get the 110kV Source fault level, the percentage impedance of the 64MVA Trf. & the type, size & length of the OH Conductor.

Register to Reply
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#4
In reply to #2

Re: Sizing switchgear according to SC current

04/19/2011 11:58 PM

The only correct way of estimating fault levels in your plant is to get the short circuit levels at the point of common coupling from the power supply utility. We will also need single line to ground fault levels apart from the 3 phase to ground fault levels, if we want to determine short circuit levels for all types of faults.

Ignoring source impedance from the utility will result in conservatively higher short circuit levels and corresponding breaker sizes [and costs]

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Register to Reply
Member

Join Date: Jan 2011
Location: bilaspur cg
Posts: 7
#5

Re: Sizing Switchgear According to SC Current

04/20/2011 4:57 AM

use the formula A = (I * sqrt of t )/k

A= Cross aection area of cable or cunductor

I=Short ckt current in KA

t = withstand time in Sec

k= Constant for Al is 0.094

Register to Reply Score 1 for Off Topic
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#6
In reply to #5

Re: Sizing Switchgear According to SC Current

04/20/2011 5:07 AM

I am sorry to say that I disagree with this formula. This is a thermal withstand rating of the equipment equation.

While selecting the breaker, the important point is the highest making and breaking capability of the breaker. This requires short circuit calculations.

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Register to Reply