Mining Transformers

04/29/2011 4:50 AM

Knocking about in our quarry were 2 or 3 ex pit transformers 100KVA 3.3/.55KV. I got involved with a couple of them when we tried to start a limestone mine (don't ask, it was meant to be a disaster from the start).

What is puzzling me is they had tertiary windings, anyone any idea why? They weren't brought out to any external termination.
The O/L and E/F protection on the LV side tripped the 3.3 OCB

God alone knows where they came from in the first place. They were from the 30's. I was resurrecting them in the 70's.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#1

Re: Mining transformers

04/29/2011 7:54 AM

Were they perhaps "taps" to adjust the output voltage for variations in the input voltage. (Presumably no tab changer, but just some extra windings that could be manually connected and used to boost or (hmm, unboost) the voltage, either at the high or low voltage side?

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2
In reply to #1

Re: Mining transformers

04/29/2011 9:07 AM

Nice idea and thanks for the suggestion, but there were no external connections to these windings. To change anything internally would be major as the tanks were Ex.

I'm beginning to wonder if they could be for fault limiting as they were for mine use.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#3

Re: Mining transformers

04/29/2011 11:21 AM

This sounds like the transformers may have been designed for extremely high voltage work. In the Tesla community, that is a goal...cheap easy HV (usually on a much smaller scale, obviously). I got this from a HV/Tesla site:

There is a solution, however. Assume a transformer with 3 windings: the 110V primary, the HV secondary, and another 110V tertiary. Also assume that the insulation of the transformer is such that the two 110V windings can take the full secondary voltage. If this is the case, then you can feed a second transformer from the first, essentially using the first transformer as a isolation transformer. The primary of the second is fed from the tertiary of the first. You can, of course, extend this ad infinitum, feeding a third transformer from the tertiary winding of the second, etc.

http://home.earthlink.net/~jimlux/hv/xfrmr1.htm

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: Mining transformers

04/29/2011 2:48 PM

If the tertiary winding is delta connected then it is there to carry the third harmonic of the exciting currents which in turn minimizes the Zero Sequence currents through the grounding system.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5
In reply to #4

Re: Mining transformers

04/29/2011 3:29 PM

Now that makes sense. Thanks RAM J

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#6
In reply to #5

Re: Mining transformers

04/29/2011 3:43 PM

In you op you stated they were not brought out. Wouldn't the delta ZSF have external taps to effect a neutral to the loads?

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#7
In reply to #5

Re: Mining transformers

04/30/2011 2:11 AM

TonyS,

What is the vector group of the transformer!

If there is not a single delta (either on primary or secondary) that confirms that the unloaded / hidden delta tertiary is for circulating the third harmonics and thus prevent them from flowing in the input power cables.

The harmonics in the cables cause disturbance in the telecom circuits, additional heating, additional voltage drop etc.

__________________
Raghunath
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#8
In reply to #7

Re: Mining transformers

04/30/2011 7:24 AM

If you read my original post you will see this is a recollection from the 70's. I found references to it in old logbooks. It's stuck in my mind since then, mainly because I got involved in a project that had to be proved wouldn't work!

The transformers are long time scrapped so I don't know the vector grouping, there're not in my log.

Harmonics in telecoms equipment is hardly going to bother mining equipment. Whereas it would with sensitive fault detection. They hadn't got the fancy relays in the 30's we have today.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Commentator

Join Date: Jul 2009
Location: chennai, India
Posts: 55
Good Answers: 1
#9
In reply to #8

Re: Mining transformers

04/30/2011 2:03 PM

Dear Mr. TonyS,

Generally, it is practice to provide a Delta- Star transformer to suppress the flow of zero sequence component of secondary side earth fault current on the upstream side,thereby limiting the operation of sensitive earth fault protection only at low voltage side of the transformer.<p>

For some economy of design the transformer would have been designed with Star -star transformation . then it becomes a must to provide tertiary delta to circulate the zero sequence current of the earth fault in the secondary side earth fault.<p>

As this was designed for dedicated purpose and to discourage anybody to use this as source for connecting any load, this circuit would have been terminated in side .

__________________
There is nothing either good or bad, only thinking make it so -
Register to Reply