05/06/2011 10:51 AM
What is accumulative kA interruption storage of 22kV switchgear?
Does switchgear have such an option to accumulate how much kA interrupted?
If have, where does this store and how we call that, a counter?
Anything that can go wrong, will go wrong
Re: Counter for switchgear
05/06/2011 11:02 AM
If you use a protection relay which it has this option(for example Sepam), you can see.
05/06/2011 11:07 AM
Oh, Sepam is used in my last project but I did not know if it has this function. So it is a standard not an option, isn't it?
India - Member - New Member
Good Answers: 164
05/06/2011 11:52 AM
One thing which never occurred to me before...
When the relay senses a fault and trips the CB, fine, it stores the data and displays on demand. Some clever ones convert it to life left also. (One full short-circuit breaking = 1/3 life gone for example)
What about when the operator trips the CB at rated current ? Does the relay note that too ? And deduct one operation from the life expectancy ?
Perhaps a stupid question, but there it is
Good Answers: 170
05/08/2011 11:13 AM
I think today's numerical relays can also measure and store the current interrupted apart from the event logging. Thus, may be, a programme is available by mesauring this current interrupted and calculating the residual life. I am equally novice at these micro things.
Good Answers: 164
05/08/2011 11:42 AM
Join the club!
i don't trust those micro-things !
If i operate a normal MCCB 5000 times on load, i doubt if i will ever know if it can take a short circuit if one came ! Even the ones with the μP relays. Unless i have a SCADA system.
So, what can one do ? i would use a fuse !!!
05/08/2011 4:08 PM
Assume the typical worst case fault current and just count the breaker operation counter. If the breaker is operating that much there is probably a system design or protection discrimination problem.
They are a useful guide, but a guide none the less.
05/08/2011 4:27 PM
This is a page of Sepam manual