64. Ground protective relay is a relay that functions on failure of the insulation of a machine, transformer or of other apparatus to ground, or on flashover of a dc machine to ground. Note: This function is assigned only to a relay which detects the flow of current from the frame of a machine or enclosing case or structure of a piece of apparatus to ground, or detects a ground on a normally ungrounded winding or circuit.
It is not applied to a device connected in the secondary circuit or secondary neutral of a current transformer, or in the secondary neutral of current transformer connected in the power circuit of a normally grounded system.
As can be seen a relay connected in the Primary Neutral Circuit or in the residual path of the Phase CTs' secondary neutral MUST NOT be given the DEvice Function Number 64. It is generaly numbered 51N, as this can also respond to phase unbalance conditions, if the unbalance is more than the setting in this 51N Relay. And, this is possible with 3-Phase, 4-Wire distribution systems,with single phase distribution, if the single phase loads connected to the phases are not distributed and/or utilised evenly.
As regards 51G, it is a time delayed realy and is aptly called "Back-up" Earth Fault Relay. Whereas 64 shall be instamtaneous only.
Unbalance had been pricking me too for so long! Thanks to some good reading! I have overcome the pricks now!
1) Now, there are three methods of connecting 51N
i) Connect 51N only in the residual path of the phase CTs only, with no neutral CT. Here, you set the 51N relay to, say, 10%. This means that even when the 51N relay sees upto 10% of its setting, it shall remain mute, an indirect way of telling the relay that upto 10% is no earth fault, but only system unbalance due to unequal distribution and/or utilistaion of phase loads.
ii) Connect 51N relay in the residual path of 3 Phase & 1 Neutral CTs. Here, the 51 N relay would sense only genuine earth faults as any phase unbalance would be offset by the neutral current fed into the relay equal in magnitude but opposite in direction. Here, the 51N relay settings can be made more sensitive.
iii) Install a CT is the Primary Neutral Bar and the secondary of this CT is connected to the 51 N relay. The scenario is similar to (i) above.
2) As explained above. If the current thro the 51N relay is less than or equal to the setting made in the relay, it is perceived by the relay as "normal" system unbalance current. Anything above is perceived to be earth fault and the relay reacts.
3) Depends upon the single phase loads distribution/utilistaion in your system.
ii) For this section, how much percent would be appropriate? In the case we have earth fault (phase touch ground), the grounding wire will carry the current not the neutral. Could you put more detials on how the relay will react in this case please?
__________________
Anything that can go wrong, will go wrong
What is the connection methodology for 64 Relay? Core Balnce CT (Zero sequence CT) is the mandatory one for 64 protection. Please, provide your advice.
Good Answers: