Commissioning of Repaired 132kv/6.6kv Transformer

05/08/2011 8:10 AM

What are the proceedures to improve PI value of 132kv/6.6kv transformer to the required level ie. 1.8 to 2 ?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: Commissioning of Repaired 132kv/6.6kv Transformer

05/09/2011 12:05 PM

Drying Out!

Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Commissioning of Repaired 132kv/6.6kv Transformer

05/09/2011 1:37 PM

..and contacting the manufacturer and/or a competent transformer engineer. The PI (Polarity Index) is just one measure of the transformer's insulation "health", if it is multiples above 2.0 then chances are the insulation is wet or dirty. Hopefully you have checked the DP (Dew Point) and BDV (Break Down Voltage) of the oil, done a DGA (Dissolved Gas Analysis), OA (Oil Analysis), pulled a vacuum, put on a nitrogen blanket, etc. prior to your PI test. Not all are necessary if the transformer was in service prior to the poor PI test, but if it has been severely overloaded, opened and/or the nitrogen blanket breached then PI might not tell the whole story.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#3

Re: Commissioning of Repaired 132kv/6.6kv Transformer

05/10/2011 1:00 AM

First conduct the test on Oil.If its break down value is lower then use a filter machine and do it till moisture is removed.Clean all bushings with CTC.If above is not giving satisfactory results you have to dry out the winding by heating by circulating acurrent by applying a low voltage.Normally a welding generator can balso be used to get a suitable current which can give higher current at lower voltage.Then u have to do all precommisisiong tests

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #3

Re: Commissioning of Repaired 132kv/6.6kv Transformer

05/10/2011 1:55 AM

I think CTC (carbon Tetra Chloride) is banned. Even if it is not, you will be doing a great harm to the environment if you use CTC. One can go for CRC 226 instead.

Reply
Reply to Forum Thread 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (2); nesubra (1); RAMConsult (1)

Previous in Forum: Protection Relays Coordination   Next in Forum: Phasing Out Procedure

Advertisement