Explosion Venting

05/11/2011 3:05 PM

We have to test an explosion vent that has a release pressure of 25lbs/sqft. Each unit has 2 doors and each door has an area of 3' x 10'. These units are nothing more than a door under a great amount of sprung force that is held in place on a trigger plate, 1 trigger per door. When enough pressure (25lbs/sqft) is built up on the doors surface, due to an explosion, the mechanism that pushes the trigger plate will release the door and the spring will assist in keeping the door open. This allows the explosive force to exit the building through the vents without causing damage to the structure.

I have been told that the mechanism should be tested to release at 25lbs of pull force and this will remain constant no matter what the size of the door is. I would think that you would calculate the total sqft of the area of the door and that would be the force required to release the trigger plate. 10x30=300x25=7500lbs but this sounds like a lot of force and what force gauge would messure that amount?

Any ideas would be very helpfull.

__________________
Thank you everyone for all your feedback.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Explosion Venting

05/11/2011 3:37 PM

The trigger mechanism can be the same value, regardless of the door size, and so can the area of the trigger initiator because it is the "initiator" and not the actuator.

It doesn't open the door it just lets the mechanism work after the door is open to keep it open. The actuator can be sized according to door weight since the doors will be opened by the blast.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Dec 2010
Posts: 166
Good Answers: 4
#7
In reply to #1

Re: Explosion Venting

05/12/2011 11:55 AM

I remember a demonstration in 5'th grade involving an empty paint can, votive candle, rubber tube and small amount of flour. Bounced the lid off the cieling. Very impressive and memorable but try doing that today. The kids will be getting their master's by the time you get the permits.

Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#2

Re: Explosion Venting

05/11/2011 4:09 PM

I am trying to understand your question fully... The only question you ask is "...what force gauge would messure that amount?" I am not certain this is the real question. Would you consider a few questions from me:

"We have to test an explosion vent that has a release pressure of 25lbs/sqft." Are you an independent certification lab? That is to say, why do you have to do this test?

When you perform this test, what fuel source or combination are you going to use for the deflagration? What... no explosion? I was sort of looking forward to watching that.

Do you have a copy of NFPA 68? Have you read it?

__________________
Semper Ubi Sub Ubi
Register to Reply
Member

Join Date: Nov 2007
Location: Toronto Ontario Canada
Posts: 5
#4
In reply to #2

Re: Explosion Venting

05/12/2011 9:49 AM

Thank you for all the input as it was quite helpful. I am sorry if my question wasn't clear as I am just a laymen, as you might have figured, but the actual question is how do I test this unit if it is claiming to open at 25lbs/sqft. Do I just hook on a force gauge, give it a tug and the door should open with a force of about 25 lbs? We do not have access to an air cannon and there are too many units, 60 in total, that are about 60 feet off the ground on a storage facility to hook up anything from below. We have to maintain the building and we want to make sure that they open as required, for safety and insurance reasons. We could presssurize the building but that seems a little excessive if all we need is a force guage.

__________________
Thank you everyone for all your feedback.
Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#5
In reply to #4

Re: Explosion Venting

05/12/2011 10:08 AM

These expolsion relief vents...

Are the devices a manufactured item? With a manufacturers nameplate, compliance data, date of manufacture, etc. If yes, what does the manufacturer have to say? If no, do you have the original fabrication data and design spec?

I know this is not really your question, but it will be useful to know if the original design was within your required performance today.

__________________
Semper Ubi Sub Ubi
Register to Reply Score 1 for Good Answer
2
Active Contributor

Join Date: Jun 2010
Posts: 14
Good Answers: 2
#6
In reply to #4

Re: Explosion Venting

05/12/2011 10:59 AM

Do the math from the pressure point of view. 25lbs/sqft=0.17psi or 0.012bar. Very low, but then it doesn't take a large overpressure to damage a building.

25lbs over 3'x10' is 0.833 lbs/sqft = 0.0058psi or 0.0004bar. A good gust of wind could open that panel. What about someone leaning against the door from inside?

25lbs/sqft is a typical explosion vent trigger value, and you will need to test the trigger at 750 lbs for your 30sqft doors.

Look at this link, it talks about a commercial explosion vent and what force would be required to open them. (Scroll down to the last item on the page.)

http://www.c-sgroup.com/explosion-vents/faq

Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#8
In reply to #4

Re: Explosion Venting

05/13/2011 5:18 AM

Do I just hook on a force gauge, give it a tug and the door should open with a force of about 25 lbs? No, the force unit is lbs/sqft. So, calculate the area of explosion door in sqft and multiply with 25 lbs to get required force to just hook on a force gauge to test. For example if area is 10 sqft, you have to hook 250 lbs. With this calculated load if door is not opening, then its weight is to be reduced. If opens with less load, weight is to be added.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Aug 2010
Location: Melbourne, Australia
Posts: 740
Good Answers: 24
#3

Re: Explosion Venting

05/12/2011 12:35 AM

You could test them with controlled releases from an air cannon (similar to those seen on Mythbusters) sealed to their housing and with pressure monitors installed.

This would give you control, adjustment, measurability and a realistic scenario.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#9

Re: Explosion Venting

05/14/2011 3:29 AM

With all my dealings with explosion doors we called the manufacturers in to test them. Simply to get the insurance cover.

After seven explosions in one night, I'm just glad they worked!

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Doorman (2); Gazu (1); H2girl (1); lyn (1); meikermann (1); pritam (1); TonyS (1); WAWAUS (1)