Air Circuit Breaker

05/12/2011 10:07 AM

What will happen if we connect 3Phase for 4pole Air circuit breaker by keeping nutral open

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Aircircuit breaker

05/12/2011 10:16 AM

1. The fact that you have spent extra money for a 4-pole ACB implies that you need the neutral to be switched also.

2. It is not a good practice to keep the neutral open, it may give rise to floating neutral and other undesirable consequences.

3. You can run the neutral through directly, without connecting it to the 4th pole. It will work ok. Except that you cannot open the neutral if required (for switching over to a standby supply for example). But then, why was the 4-pole ACB ordered?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Active Contributor

Join Date: Mar 2011
Posts: 22
#2

Re: Aircircuit breaker

05/12/2011 10:31 AM

But unfortunatly we got this 4pole breaker because ups require 3pole only. what to do.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: Aircircuit breaker

05/12/2011 10:40 AM

Are you sure about the UPS being only 3 pole? i am surprised. When you have a UPS, my understanding is that you MUST break the neutral. i have not gone into the depth of why, but some experts will doubtless enlighten us.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#8
In reply to #3

Re: Aircircuit breaker

05/15/2011 10:27 AM

I fully agree with KVS! It is dangerous not to break the neutral. Imagine you have switched off the 3-pole breaker for some maintenance on the UPS! At the same time if there is an earthfault elsewhere in the system, a portion of the earth fault current would circulate thro this unbroken neutral and cause dangerous potential rise inthe UPS neutral thus endangering any person working on the UPS. Please break the neutral for God's sake.

Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#4
In reply to #2

Re: Aircircuit breaker

05/12/2011 10:55 AM

What relationship of this 3-pole UPS and the 4-pole breaker?

__________________
Anything that can go wrong, will go wrong
Register to Reply
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#5
In reply to #4

Re: Aircircuit breaker

05/12/2011 11:19 AM

Cousins by marriage

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply Score 1 for Good Answer
Anonymous Poster #1
#6
In reply to #5

Re: Aircircuit breaker

05/12/2011 11:28 AM

Awesome answer to one of the most inane posts i have ever seen

Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#7

Re: Aircircuit breaker

05/12/2011 11:17 PM
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Register to Reply 8 comments

"Almost" Good Answers: