I make my calculation for STP plant . My load calculation consist of total 5 pumps .The description as follows :

During continuous operation :

1). duty loads :2 nos & 1 stand by .

2). Duty load : 1 no.

3). Duty load : 1no.

My first two pumps will start each Full load amp is 54A .Therefore 2x54 = 108A .

My third pumps (FLA : 91) will start (biggest load - DOL starting only) ,I considered 6times starting current(6x91=546A) therefore the load at starting will be as 108A+546A = 654A which will be starting current after a certain time my continuous load will be 108+91=199.Know

My fourth pump (FLA : 91) will start (biggest load - DOL starting only) same as i considered starting current 6 times therefore the load at starting will be 108A+91A+546A=745A) which will be the starting current after a certain time my normal load will be stable to 108A+91A+91A=290A , know the total load of the plant at continuous running is 290A .But if you think technical my starting load of the biggest motor adding the load coming 745A in this case i selected the main breaker size of NS630/STR23SE could any one help me out is the selection of the breaker is the biggest size of it should be possible to use less size of the breaker with NS400/STR23SE .Please give me technical answers for the mention subject.The type of breaker selected is from MERLIN GERIN.

My question is that what should be the best practice/rule of thumb during selection

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Breaker Sizing

05/17/2011 2:50 PM

If you were using the NEC you would size the breaker as follows:

250% of the largest motor + the FLA of the other motors.

Based on this you have 250% x #3 + #1 + #2 +#4

2.5 x 91 + 54 + 54 + 91 = 228 +54 +54 + 91 = 426 amps. Go to next size = 500 amps.

conductor 1.25 x 91 + 54 + 54 + 91 = 313 amps. Depending on VD you may want to increase size of the conductor.

Register to Reply Good Answer (Score 3)
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: Breaker Sizing

05/17/2011 6:51 PM

It is a good answer. This refers to NEC 430.62. Here is also a related thread with supporting this answer: http://cr4.globalspec.com/thread/44485. This refers to NEC 430.62.

Note: 250% of the large motor FLA can be used if the breaker is 'Inverse Time Delay'. For 'Instantaneous Trip' breaker 800% of large motor FLA can be used (refer to NEC Table 430.52).

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Breaker Sizing

05/19/2011 4:56 AM

It is always a better practice to size the Incomer ACB as per the full load rated current of the transformer plus a 10% cushion - irrespective of the total connected load or the total operating load. So, if your transformer is, say, 1000kVA, then the 415V ACB has to be sized to 1333 + 133 = 1466A, the nearest size available being 1600A.

This is to avoid replacing the ACB, if you connect any additional loads in future.