Wet Test for Cables

05/18/2011 6:03 AM

Hi all friends.

I saw most cable factory do a wet test for cables. There are a few question I am not sure why and how.

First Q: what kind of cable do we need to do the wet test?

Second Q: why should we connect the +ve lead to the earth and -ve lead to the conductor of cable?

I asked a couple engineers about the 2nd question, they can not tell me why, they said it is in their specification. and they did the connect for years.

I wish one of you can tell me why, and where I can find a reference standard.

any comments about wet test are welcome.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Wet Test for Cables

05/18/2011 11:10 AM
Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2
In reply to #1

Re: Wet Test for Cables

05/18/2011 12:03 PM

Nice one!

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Wet Test for Cables

05/18/2011 12:47 PM

That should be required reading for every first time poster.

Register to Reply Score 1 for Off Topic
Member

Join Date: May 2011
Posts: 9
#5
In reply to #3

Re: Wet Test for Cables

05/18/2011 10:45 PM

If all answers r available on the internet, or even there is an answer, if everyone find the answers by searching. We won't have forum such as cry4 anymore. We won't need forums. U can tell me the answer if u knew it. Sure you don't hv to . I am expecting others. I always think there is no stupid question at all. There is only stupid people does not want to ask question.

Register to Reply
Anonymous Poster #1
#6
In reply to #5

Re: Wet Test for Cables

05/19/2011 4:22 AM

Don't worry about it. A few around here seem to be suffering Guest postpartum. AKA someone to belittle. Just take heart in that if they actually think they know they will generally be bursting to answer with some sort of information. Otherwise just assume they don't know.

Joining the conductors 'might be' so you have one circuit in series to test verses a detector conductor ...

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#9
In reply to #5

Re: Wet Test for Cables

05/19/2011 11:11 AM

I think CR4 will be around for a long time. Fortunately there are enough legitimate questions to keep most interested.

Unfortunately, there will always be those who ask questions like "if my operator tells me he has gauge that fluctuates what I do?"

It is painfully obvious that many people come here first before doing even the most elementary search for themselves.

Cheers.

Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#10
In reply to #9

Re: Wet Test for Cables

05/19/2011 11:42 AM

Re: Unfortunately, there will always be those who ask questions like "if my operator tells me he has gauge that fluctuates what I do?"

I have no problem with that. I'd like to help him. If that's where he's starting from, so be it.

(Help might result in a variety of resolutions--he might decide he needs to get some formal education, he might decide he needs to switch careers, he might learn to search elsewhere on the Internet, or, of course (and unfortunately), he might end up hurting himself or others. (I hope not, and will do what I can to avoid that.) (I haven't tried to think of all the possible outcomes.)

He might have a good education, but never have dealt with an operator, or a problem, or a chance to think for himself. (Or he might have little or no education, yet also never dealt with an operator, ...

Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#4

Re: Wet Test for Cables

05/18/2011 8:43 PM

When all else fails, ask the instructor. That's what they get paid for

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply Score 1 for Off Topic
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#7

Re: Wet Test for Cables

05/19/2011 7:11 AM

dear,

IS clearly explains the procedure for wet test.

2> probably, this is related to the test set up. Just, there are 2 systems - negative earth system / positive earth system.

Your test set up must be with positive earth system. Can you please mail the drawing of test set up? that will answer.

__________________
Exploring the Science of Electricity
Register to Reply
Member

Join Date: May 2011
Posts: 9
#11
In reply to #7

Re: Wet Test for Cables

05/19/2011 10:13 PM

there are too many bla bla ders around. they should be on talk show, not in the technical forum.

HI hurry,

you are right, we use the positive earth system for the test. BUT the negative earth system works as well.

specification recommends the positive earth system without a reason.

Do you know any benefits with the positive earth system?

I found corrosion may be an issue. but this would not be a concern for the cable insulation resistance test. would the spec still rrecommended a positive earth system?

Register to Reply
Member

Join Date: May 2011
Posts: 9
#13
In reply to #11

Re: Wet Test for Cables

05/19/2011 10:40 PM

hi harry,

thankz for your hint.

sorry for calling you "hurry".

Register to Reply
Guru
Popular Science - Weaponology - New Member Fans of Old Computers - PDP 11 - New Member Technical Fields - Architecture - New Member Hobbies - HAM Radio - New Member

Join Date: Oct 2009
Location: Maine, USA
Posts: 2168
Good Answers: 71
#8

Re: Wet Test for Cables

05/19/2011 10:57 AM

I hate it when someone tells me "because we always do it this way" as an answer to a valid question of "why do you do that?". If you can get access to their specifications you may find the answer there.

__________________
Tom - "Hoping my ship will come in before the dock rots!"
Register to Reply
Member

Join Date: May 2011
Posts: 9
#12
In reply to #8

Re: Wet Test for Cables

05/19/2011 10:38 PM

people on the same position for years, they have learnt how to follow the routine with out asking any questions.

teh standard spec only tells how to do , and what to do. but it doesnt tell WHY.

the specification only recommended the positive earth system.

Register to Reply
Member

Join Date: May 2011
Posts: 9
#14

Re: Wet Test for Cables

05/19/2011 10:57 PM

time to stop this topic,

Register to Reply Off Topic (Score 5)
Register to Reply 14 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); dj95401 (1); harry potter (1); lyn (3); qli029 (5); rhkramer (1); Tom_Consulting (1); TonyS (1)