Lightning Protection for Chimneys

05/19/2011 2:19 AM

For our 250 Tonn boiler chimney ( concrete) we are installing lightning arrestor.The copper earth conductor has to be brought down and to be connected to earth pit.For our metal chimneys we have provided insulators wherever necessary for the copper flat.Is it necessary to insulate the copper down conductor for Concrete chimney.Why the copper flat cannot be fixed directly on the concrete chimney without insulators.

Pl clarify.

T.Sriram

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Lightning protection for chimneys

05/19/2011 3:48 AM

The insulators hold the flat in place without the need to drill and therefore doesn't reduce the CSA.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
7
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Lightning protection for chimneys

05/19/2011 4:52 AM

You are dictated by incorrect practices.

Vide IS 2309, if the structure is made of a conductiave material, then there is no need to run a Copper Down Conductor. The structure itself will act as the down conductor. So, your metal chimney need not be run with any copper down conductors.

In case of a non-metallic chimney too, the insulators you are providing are only COSMETIC. Because, based on my experience, I have seen people installing either a small porcelain insulator or a small SMC Insulator while fixing the Lightning Down Conductor to the Structure. The voltage rating of this insultaor - at the maximum - is only 1.1kV. Whereas, when a Lightning strikes and the conductor disacharges a current, based on the Lightning System Earthing Impedance, the potential difference (across the "so-called" insulator) between the down conductor and the structure on which it runs - might reach very high values, of the order of 10kV or more. The cosmetic insulators provided would definitely explode. I have seen enough such damages.

So, the best practice is to "bond" the structure and the down conductor (i.e.) to lay the down conductor right on the concrete structure of the chimney, without any intervening insulators. Thereby, you are creating an equi-potential plane and there will not be any brekadowns, during a lightning discharge.

Register to Reply Good Answer (Score 7)
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#3
In reply to #2

Re: Lightning protection for chimneys

05/19/2011 6:32 AM

dear,

In this case , the % of lightening stroke flowing inside the structure / building shall be more. definitely, these cosmetic insulators if height- 50 - 60 mm, it with stands the part of lightening stroke, allowing less surge currents to flow inside the structure, minimising the risks of damages due to leakege currents during lightening.

May be damaged insulators might have performed the Z catagory protection !

__________________
Exploring the Science of Electricity
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #3

Re: Lightning protection for chimneys

05/19/2011 10:21 AM

Well! Between the spans of these cosmetic insulators, the insulation between the structure & the down conductor is air at atmospheric pressure. Even though the insultaor might just withstand - which, I doubt, the potential rise during a lightning stroke, definitely the air insulation would not withtsand and there could be hevay flashover.

Reference is also drawn to Figure 12 of IS 2309, wherein the down conductor is cliped on to a brick chimney wall without any insulator - cosmetic or otherwise. And, vide Clause 12.5.1 of IS 2309, bonding is recommended rather than isolation, when a conductor is run on a structure.

As regards a metallic chimney, reference is drawn to Clause 12.5.3 (b): "where a structure is simply a continuous metal frame, it requires no air terminaltion or down conductor"

Since you are from India, I suggest you read the Indian Standards, before countering any answers which I quote from the Standards.

Register to Reply
Anonymous Poster #1
#7
In reply to #4

Re: Lightning protection for chimneys

05/19/2011 11:38 AM

Good one, EE65.....

And harry, please. For God's sake.
Stop calling the whole word "DEAR" ... restrict it to those who are in relationship with you..

Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#10
In reply to #7

Re: Lightning protection for chimneys

05/20/2011 3:22 AM

dear,

cool down buddy....

some times hot discussions requires cooling .....

__________________
Exploring the Science of Electricity
Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#11
In reply to #4

Re: Lightning protection for chimneys

05/20/2011 3:32 AM

Dear,

This is not the issue with metal structure - this is for RCC structure.

If there is a flash over in between the conductor, better check the Earthing quality of the earth electrodes.

It is established universally that even a good quality earth provided to the lightening conductor, there will be a leakage of electricity in side the building strucure - & thru this, to electronic equipments like intercom etc.. get damaged by lightening surge voltages. Many times causing danger to the human life thru leakage currents in the strucure walls - that may pass thru human body in contact.

__________________
Exploring the Science of Electricity
Register to Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#5

Re: Lightning Protection for Chimneys

05/19/2011 10:55 AM

Concrete armour WILL conduct more of the lightning charge than it (and surrounding concrete) can thermally handle. That would be desastrous for the stucture's integrity. S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Guru

Join Date: Mar 2011
Location: Sebastopol, California
Posts: 1205
Good Answers: 54
#6

Re: Lightning Protection for Chimneys

05/19/2011 11:28 AM

I would insulate it. Concrete is more conductive than you may think at high voltage. The large current of a lightning strike could shatter the matrix by suddenly driving off the water.

My mother was almost killed by a chimney strike on a brick chimney. Shattered the mortar and the brick....

The insulation will protect the masonry from the sudden heat as much as from the current.

__________________
Most people are mostly good most of the time.
Register to Reply
Guru

Join Date: Aug 2010
Location: Melbourne, Australia
Posts: 740
Good Answers: 24
#8

Re: Lightning Protection for Chimneys

05/19/2011 11:32 PM

One other point which you have not asked and has not been mentioned previously:

The Lightning arrestor should be a straight run down the chimney to the earth point with the minimum possible bends and certainly no sharp or small radius bends.

In a lightning strike the current in the arrestor is huge and any bend present a significant inductance. Any bends will result in a high potential at that point and probably a flash-over to any nearby conductor.

Register to Reply
Guru

Join Date: Jun 2010
Posts: 989
Good Answers: 14
#9

Re: Lightning Protection for Chimneys

05/19/2011 11:54 PM

the lightning will jump to the re-bar and blow chunks of concrete out of the chimney.

Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#12

Re: Lightning Protection for Chimneys

05/21/2011 8:51 AM

Principally because the lightening conduction is a half cycle 'skin effect'.

So spacing it off the surface is pertinent to protecting the surface - be it 'conducting' at a lesser conductivity, or 'nominally insulating' - like brick or reinforced concrete.

The overarching idea is the 'ground conductor' is cheaper to replace than the structure, or you wouldn't bother.

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

129CBRider (1); 34point5 (1); Anonymous Poster (1); Deefburger (1); electricalexpert65 (2); harry potter (3); SimpleMind (1); TonyS (1); WAWAUS (1)