Relationship Between Voltage Drop and Power Factor

05/26/2011 3:28 AM

Require Guidance for Cable Voltage Drop with respect to P.F:

% Voltage drop = (1.732X Full Load CurrentX Length (Km)X(Rcos@+Jsin@)X100 )/ (Volt X No of Run)

Ex. For 1.6KM , 50Amp,cos@=0.8,Sin@=0.6, R=0.41Ohm/Km, j=0.074Ohm/Km

% V.D =12%

But if P.F will increase and goes to 0.9 (Cos@=0.9) than

% V.D is 13.40%.

so if System has Good P.F than You have more Voltage drop..If we installed Capacitor Bank to minimise KVAR hece to improve P.F will increase V.D in System..

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Jan 2011
Location: Jakarta
Posts: 162
#1

Re: Relasionship between Voltage drop and Power Factor

05/26/2011 4:14 AM

Hi,

I better look cable manufacture catalog to find the voltage drop than calculate.

__________________
One system
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: Relasionship between Voltage drop and Power Factor

05/26/2011 5:18 AM

Doesn't seem logical does it? When the pf is 1, the current is the least. It goes up as the pf comes down. The voltage drop depends directly on the current for a given set of conditions. How can it go up as the current goes down?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Commentator
Engineering Fields - Power Engineering - Power Engineering Passion Engineering Fields - Electrical Engineering - Engineering Passion India - Member - New Member

Join Date: Mar 2011
Location: Noida, (U.P.), India.
Posts: 99
Good Answers: 6
#3

Re: Relasionship between Voltage drop and Power Factor

05/26/2011 5:38 AM

Single phase voltage drop:

Vd = 2K x L x I / Cm or Cm = 2K x L x I / Vd

For both examples: Vd = voltage drop, K= 12.9 for resistance for a copper conductor, L = length of circuit in ft., I = current or amps of the load, Cm = area of the conductor in Circular Mills.

Three phase voltage drop:

Vd = 1.73K x L x I / Cm or Cm = 1.73K x L x I / Vd

1 square mm = 1973.52524139 Cm or Circular Mill

__________________
Sure Answers Always
Register to Reply
Anonymous Poster #1
#4
In reply to #3

Re: Relasionship between Voltage drop and Power Factor

05/26/2011 6:09 AM

What has this got to do with the OP???

Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Relasionship between Voltage drop and Power Factor

05/26/2011 7:36 AM

I fully agree with KVS. When the power factor has improved from 0.8 to 0.9, then definitely the current thro the cable also MUST have reduced from 50 Amps to a lesser value. I think, in your case, you have taken the current as 50 Amps in both the cases.

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (1); kvsridhar (1); loadshare (1); Vinu_Answers (1)