Genset Problem

05/26/2011 10:43 AM

we have problem in genset 325kva without PMG operated in parallel with another tow gensets 300kva with PMG the problem is when the three gensets operated in parallel G3 (325 kva) the KW meter is 100 kw and current current meter is 300A and G1&G2 the KW meter is 100kw and current meter 150 A and when the load transfer to the main the G3 trip with revers power alarm we closed the droop to end limit

__________________
atef
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: engineer atef

05/26/2011 1:13 PM

Your problem has little to do with the type of excitation system and much to do with the fact that your gen sets' control systems are not interconnected properly. Although you do not supply enough information to determine the exact mode of operation the fact that the two older gen sets are picking up less than the expected portion of the load generally means that there is no coordination between systems. The governors and the AVRs (Automatic Voltage Regulator) need to be set for parallel operation with the proper droop/compensation settings.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Member

Join Date: May 2011
Posts: 7
#2
In reply to #1

Re: engineer atef

05/28/2011 7:47 AM

actually we setting the governor and AVR of G3(new genset)I want to ask, is the absence of PMG is the cause of this problem Or has no effect

__________________
atef
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3
In reply to #2

Re: engineer atef

05/28/2011 1:50 PM

Again, although different types of excitation systems have different operating characteristics and response times, proper tuning accommodates those differences. The absence of a PMG should make no difference if the control systems are properly set up.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Member

Join Date: May 2011
Posts: 7
#4
In reply to #3

Re: engineer atef

05/29/2011 4:00 AM

I need to know why G3 current reach to 300A at 100 kw this value accepted or no and what is the reasons which cause the reverse power problem in G3 please confirm

__________________
atef