Sucker Rod Pumps Effected on Generators

06/05/2011 4:13 AM

We have many oil production wells which using sucker rod pumps to lift the oil,but we have a problem appeared in main power station or stand alone generators , there are fluctuation in HZ and amperage consumed from the power units ,the attached files shown this fluctuation

we need advice to solve this problem because we face a problem to get two generating units or more run in parallel .

  • Sucker rod pumps (variable load),the attached file show the fluctuation in power for (motor 100 H.P) .
  • And from attached file you can note that.
    1. The fluctuation in frequency from 48 to 52 HZ according to SRP frequency fluctuation attached file.
    2. There is regenerative power during normal operation which cleared in SRP power fluctuation attached file
    3. The current fluctuation between 57 and 105 amp according to SRP current fluctuation attached file.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: City of Light
Posts: 3943
Good Answers: 183
#1

Re: Sucker Rod Pumps Effected on Generators

06/05/2011 6:30 AM

?????????????????????????????????????????????????????????????? Attached ????

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Sucker Rod Pumps Effected on Generators

06/05/2011 10:55 AM

Without seeing the attached(?) files my guess is that the total load is too closely matched to the gen set ratings. Widely varying cyclical loads such as the sucker pumps can cause hunting in governors, this problem is further aggravated by the harmonics caused by reciprocating engines, and to make matters worse there is the possibility that the random nature of the varying pump loads can cause unanticipated peaks and valleys in the overall demand when they are aligned.

The goal is to increase the robustness of the power supply. Easiest solution, not cheapest, is to add generation, but finding an expert in governor tuning may provide some relief.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Associate

Join Date: Apr 2011
Location: Located in INDIA.Kerala state,kottayam Dt,pala.
Posts: 42
#3

Re: Sucker Rod Pumps Effected on Generators

06/05/2011 11:53 AM

Sucker pump is reciprocating.So add more than one pump to the generator.So that current flow will be near uniform.Also correct power factor.Flywheel of engine to be made heavy.

__________________
Lalithambika
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#4

Re: Sucker Rod Pumps Effected on Generators

06/05/2011 12:06 PM

The big oil pumps we have here tend to have a heavy load for part of their pump cycle then produce a regenerative feedback though another part so given that type of load cycling its doubtful that you will ever completely eliminate the frequency variances completely unless your generator system is built to be many many times bigger than what the overall load it is supplying.

I suspect that due to the slightly different loads on each well the induction motors will each have a slight speed variance of +- an RPM or two from lightest loaded to heaviest loaded which over time will tend to create times where the majority of the pumps are all drawing power and then returning returning power at or near the same time.

To me I would not worry about a few Hz variance if its not affecting the overall operation of the system unless the load imbalances is at time pushing the generators well beyond its designed peak momentary capacity to the point of overheating the unit.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Sucker Rod Pumps Effected on Generators

06/06/2011 8:26 AM

In one of my earlier plant experiences, I had a similar problem. My generator literally shifted by about 15 degrees - when a reciprocating pump was run on it. We strengthened the generator foundation by increasing the number of AVM Pads (from 8 x 800 kg pads to 12 x 1200 kg pads). And... the vibrations stopped.

Register to Reply
Commentator

Join Date: May 2010
Location: UK
Posts: 89
Good Answers: 2
#6

Re: Sucker Rod Pumps Effected on Generators

06/08/2011 6:17 AM

I have sent you a email...

but unitl you reply maybe you need to check the braking resistors on the units, find out how much it would be to replace the existing motors with higher efficiency ones and get your pumps work opposed to each other, that is, one on the downstroke while the other is on the up stroke.

Your Hz fluaction could be a problem with the gen set(s) itself, get it checked and ensure the output Hz & volts is correctly monitored.

As for the power station problems, depending on the amount of pumps you are using and if you have other demands on the system, you could be experiencing high level of harmonics, negative KVar's plus no pf correction or very little, however I would like to discuss this separate from CR4, so I comply with the rules of the forum

Register to Reply