Hydraulic Valve Calibration

06/18/2011 2:31 AM

Dear I have Proportional directional valve, pilot

Operated with electrical position Feedback

I need to calibrate the valve please do we have any procedure. I am a electrical/ electronic person to handle this job

Please provide me a procedure or steps to do it

Complete valve number:- 4WRKE16E200P-38/6EG24ETK34/A1DR

MAKE REXROTH

I will be thankful for the same.

Register to Reply
Pathfinder Tags: HYDRULIC
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster #1
#1

Re: HYDRULIC 4WRKE VALVE CALEBREACTION

06/18/2011 2:42 AM

Ooh, my dear, please kiss me!

Should boldface text be considered as more (or less) shouting than ALL-CAPS?

One way to calibrate such a valve would be to measure the flow of hydraulic fluid through it at various degrees of opening.

Register to Reply
Active Contributor

Join Date: Dec 2009
Posts: 20
Good Answers: 1
#2

Re: Hydrulic 4Wrke Valve Calebreaction

06/19/2011 3:31 AM

Nomally all Rexroth valves with integral electronics will be factroy set, not to be distrubed during installation. Only zero point (p -a & p - b) can be adjustable, but not required for new valve. Hope you are having Rexroth data sheet with you, if not check the below link

http://www.boschrexroth.com/various/utilities/mediadirectory/index.jsp?publication=NET&language=en-GB

The speed and ramp to be set through PLC, not with the valve.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#3

Re: Hydrulic 4Wrke Valve Calebreaction

06/19/2011 8:16 AM

Normally followed procedure for calibration of control valves is to start with full close position and give command to open 25%, 50%, 75% and full open in steps. Compare with the actual valve position at site for each step, it should match. Repeat the same steps in reverse order from full open to full close, if it matches again then it is calibrated.

Register to Reply
Active Contributor

Join Date: Jul 2010
Posts: 12
#4
In reply to #3

Re: Hydrulic 4Wrke Valve Calebreaction

06/21/2011 3:37 AM

thanks for support from all of you i got the clear infomation as needed.

but please help me for one more concern is if the valve operating pressure is 200 bar

what is the standard pressure we can do calibration? i mean to say is pressure can make a defrence so as we care calibrating flow.

thanks for all once again for such a nice support

best regards

kailash

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#5
In reply to #4

Re: Hydrulic 4Wrke Valve Calebreaction

06/21/2011 10:11 AM

200 bar pressure may be for process pipe, not for operating the valve. Calibration can be done either at no pressure or at any pressure up to operating pressure on both upstream and downstream side. But if you want to start opening the valve from full close condition when upstream pressure is 200 bar & downstream pressure is much lower then follow process operating instructions.