Allowable Resistance of Motor Insulation and Cable Insulation

06/23/2011 2:59 AM

What is the allowable resistance of motor windings insulation and also Cable/Conductor insulation in Megger Test?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster #1
#1

Re: allowable resistance of motor insulation and cable insulation

06/23/2011 3:10 AM

As Carl Sagan would put it, billions and billions of ohms.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: allowable resistance of motor insulation and cable insulation

06/23/2011 3:18 AM

A very old rule of thumb I was given as an apprentice was that the leakage current should not exceed 1/10000th of the full load current. So just use Ohms law for the calculation.

This was based on the M&Q Act 1956, I was less than a year old!

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
3
Participant

Join Date: May 2011
Posts: 2
Good Answers: 1
#3

Re: allowable resistance of motor insulation and cable insulation

06/23/2011 4:19 AM

IEEE 2000-43 states 100 Mohm anything less on high voltage motors is a concern. We also use a rule of thumb for motors that is pre 1970 and our cables that for every 1kV (on Nameplate) = 1 Mohm + 1 so say its a 6.6 kV motor the minimum Mohm reading one should get is then 6.6 Mohm + 1 = 7.6Mohm

Also use your PI values to look at insulation integrity.

Register to Reply Good Answer (Score 3)
Associate

Join Date: Feb 2011
Location: Pune, Maharashtra, India
Posts: 32
Good Answers: 2
#4

Re: Allowable Resistance of Motor Insulation and Cable Insulation

06/27/2011 9:49 AM

As per IEEE minimum is kV + 1 Mohm as informed by our members, but, if you go for inspection then insist for value of 2MOhm per kV. This is industrial practice. If equipment insulation is in good condition this practice will not let you fail, instead you will be very sure that eqpt insulation is in good condition.

__________________
Engineering is an APPLICATION..
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Allowable Resistance of Motor Insulation and Cable Insulation

06/27/2011 11:09 AM

As per IE Rule 48, the minimum insulation resistance for low voltage installations is 1 Mega Ohm when tested with a 500V megger and for high voltage installations it is 5 Mega Ohms when tested with a 2500V megger. However, in case of motors, I would rather be more interested in checking the PI (Poarisation Index) value rather than plain insulation resistance.

Register to Reply
Associate

Join Date: Feb 2011
Location: Pune, Maharashtra, India
Posts: 32
Good Answers: 2
#6
In reply to #5

Re: Allowable Resistance of Motor Insulation and Cable Insulation

06/27/2011 2:41 PM

Just a small correction, as per IS (i Will tell exact number tomorrow), LV installations is checked with500V as you said and HV with 5000V not with 2500V. I agree about PI bur, megger is common routine test for all equipments.

__________________
Engineering is an APPLICATION..
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7
In reply to #6

Re: Allowable Resistance of Motor Insulation and Cable Insulation

06/27/2011 8:39 PM

I reproduce below the IE Rule 48:

48 Precautions against leakage before connection-

(1) The supplier shall not connect with his works the installation or apparatus on the premises of any applicant for supply unless he is reasonably satisfied that the connection will not at the time of making the connection cause a leakage from that installation or apparatus of a magnitude detrimental to safety. Compliance with this rule shall be checked by measuring the insulation resistance as provided below:

(i) All the electrical equipment shall have the 'IR' values as stipulated in the relevant Indian Standards.

(ii) At a pressure of 500V DC applied between each live conductor and earth for a period of one minute, the insulation resistance of low-voltage and medium voltage equipments shall be at least 1 MEGA-OHM or as specified in the relevant Indian Standard.

(iii) At a pressure of 2.5kV DC applied between each live conductor and earth for a period of one minute, the insulation resistance of high-voltage equipments shall be at least 5 MEGA-OHM or as specified in the relevant Indian Standard.

Register to Reply Off Topic (Score 4)
Associate

Join Date: Feb 2011
Location: Pune, Maharashtra, India
Posts: 32
Good Answers: 2
#8
In reply to #6

Re: Allowable Resistance of Motor Insulation and Cable Insulation

06/27/2011 11:05 PM

IS 7816-2002-Guide for testing insulation resistance of rotating machines Assistance for this standard has been derived from IEEE Code No. 43 'Recommended guide for testing insulation resistance of rotating machinery'

__________________
Engineering is an APPLICATION..
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#9

Re: Allowable Resistance of Motor Insulation and Cable Insulation

07/14/2011 9:34 PM
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (2); Gibson81 (1); msamad (1); Salunkhem (3); TonyS (1)

Previous in Forum: Short Circuit Calculation   Next in Forum: Comparison of 6.6 KV System vs 11 KV System

Advertisement