Differential Relay

06/27/2011 2:25 AM

how diffrential relay works in distribution transformer.what is its input.........

Register to Reply
User-tagged by 1 user
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Jun 2011
Posts: 10
#1

Re: diffrential relay.....

06/27/2011 3:38 AM

Differian Relay input is from CT's connected at Transformer both winding like for 11/0.440KV transformer 3 CT's on 11kV I/C and 3 CT at 440V O/G and relay in coordiantes between this and monitors paramers like U,I,F & Impedence of Winding . Main purpose of this relay is to monitor impedance of both the windings which effects on parameters like U,I,F & give protection in case mismatch of windings.

Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 10
#2

Re: diffrential relay.....

06/27/2011 3:43 AM

Differntial relay input is from CT's connected at both the windings like on 11/0.440KV transformer ct's are connected at 11 KV and 440V side of the transformer. This relay monitors the impedance of all windings and if any winding goes outof sync it will trip the 11kv breaker and save the transformer.

Register to Reply
Commentator
Engineering Fields - Power Engineering - Power Engineering Passion Engineering Fields - Electrical Engineering - Engineering Passion India - Member - New Member

Join Date: Mar 2011
Location: Noida, (U.P.), India.
Posts: 99
Good Answers: 6
#3

Re: diffrential relay.....

06/27/2011 5:42 AM

Differential protection is a unit-type protection for a specified zone or piece of equipment. It is based on the fact that it will operate only in the case of faults internal to the zone that the differential current (difference between input and output currents) will be high. Differential elements compare an operating current with a restraining current. The operating current (also called differential current), Id, can be obtained from the phasor sum of the currents entering the protected element:

Id = W1+W2

Differential protection is used to protect the windings of a transformer by comparing the current between the primary and secondary of transformer. if the currents are

equal then the differential protection relay will not operate; if there is a current imbalance then the differential protection relay operates.

__________________
Sure Answers Always
Register to Reply
Anonymous Poster #1
#4
In reply to #3

Re: diffrential relay.....

06/27/2011 8:09 AM

Vinu, you have been advised before.

When using material from some source you must give credit to that source, or, better still, give the link to that document so that the OP can get full benefit of that document/webpage.

Like this : http://www.emo.org.tr/ekler/ff75f52998a477f_ek.pdf

Register to Reply
Commentator
Engineering Fields - Power Engineering - Power Engineering Passion Engineering Fields - Electrical Engineering - Engineering Passion India - Member - New Member

Join Date: Mar 2011
Location: Noida, (U.P.), India.
Posts: 99
Good Answers: 6
#5
In reply to #4

Re: diffrential relay.....

06/28/2011 1:23 AM

Thanks, your suggestion will be considered. Like this,

Follow links:

http://xnet.rrc.mb.ca/janaj/differential_protection.htm

http://electricalandelectronics.org/2009/03/19/differential-protection-in-transformers/

Vinu_Answers Sure_Answers

__________________
Sure Answers Always
Register to Reply