Hi to all.
I would like to post a problem in 125VDC system. Below are the data gathered during maintenance:
Measured voltages in the DC bus:
--------------------------------------------
Pos - Neg = 130 Vdc using DC voltmeter
Pos - Gnd = 80 Vdc using DC voltmeter
Neg - Gnd = 50 Vdc using DC voltmeter
--------------------------------------------
Pos - Neg = 0 Vac using AC voltmeter
Pos - Gnd = 14 Vac using AC voltmeter
Neg - Gnd = 14 Vac using AC voltmeter
--------------------------------------------
I have tried to the following to solve the problem but I was not able to locate the source of fault:
1. Literally isolate the battery charger supplying the DC bus and battery leaving the battery banks as the DC source.
After doing this, we have ruled out the charger from the cause of this fault.
2. Inspected the DC panel looking for any sign of defects or possible loose connections or anything that may contribute to the problem.
Visual inspection was done but it will not complete the investigation.
We have noticed that the voltage between pos - gnd and neg - gnd are the same. I am suspecting that the measured AC in the DC system may be in one of the protective relays that handling AC circuits but the operating coil is DC.
Can somebody help me or give me suggestion how to locate the fault?