Transformer Neutral Grounding

07/13/2011 10:09 AM

Some power transformer neutral(Star) are earthed with Neutral Grounding Resistance(NGR) and others are directly grounded.What is the logic behind it and what should be the value of the NGR?

Register to Reply
Pathfinder Tags: transformer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Transformer Neutral Grounding

07/13/2011 2:57 PM

See previous threads on CR4 regarding this commonly-asked subject. The search function is on the right hand side of the screen.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Transformer Neutral Grounding

07/27/2011 10:01 AM

Generally Low Volatge Winding Neutrals of Transformers are Solidly Earthed and Medium Voltage Winding Neutrals are earthed through an impedance. To understand the logic, please attend to our training programme on Earthing.

The value of NGR is: Phase Voltage of the system to be earthed / desired earth fault current.