400A, 100% Rated Circuit Breaker

07/14/2011 6:27 PM

I know the code NEC 240.4(b) will allow the next size up. So you can supply a 400A breaker with 500kCMIL CU conductors. I have a 100% rated circuit breaker with 500kCMil conductors - is that code compliant?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: 400A, 100% Rated Circuit Breaker

07/14/2011 7:10 PM

Yes as long as the calculated load is 380 amps of less.

Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2

Re: 400A, 100% Rated Circuit Breaker

07/14/2011 10:02 PM

Since the cable ampacity is 380A and the next breaker ampere rating is 400A, it should comply (as also mentioned by wareagle).

But the conditions are:

(1) The conductors are not used for specific applications as defined in NEC section 240.4(G)

(2) The breaker is NEC compliant. It is not clear you indicated IEC breaker with 100% rated

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Participant

Join Date: Jul 2011
Posts: 2
#3

Re: 400A, 100% Rated Circuit Breaker

07/16/2011 2:23 AM

Just want to state that if you have circuit breaker carrying large currents or high voltages (440V AC and above), you should take the safety warnings seriously about turning them on or off causing a flash-over. At the lab I work at a guy wound up being air flighted out with 2nd degree burns and pieces of metal embedded in him when this occurred with a 440V circuit breaker. I used to think the precautions were overkill/silly before this when the lab limited people who could mess with these to be wearing clothes that don't burn (cotton, wool, silk), eye protection and leather gloves to protect hands and arms until this happened. I no longer bemoan the safety requirements they place on us.

Register to Reply