Unit Auxiliary Transformer Protection.

07/17/2011 6:19 AM

I am concerned about protection for unit auxiliary transformer for hydropower plants. I have seen normally fuse used....can 11 kV breakers be used?

Regards,

sks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#1

Re: Unit Auxiliary Transformer Protection.

07/17/2011 12:20 PM

Yes, of course a breaker is possible. But I think you mean an auxiliary transfo which is connected direct through the fuses to the output of a big generator. If you work out the fault level at this point (generator + feedback from Grid side) and get a cost for a breaker which can break that fault, to compare with the aux. transfo cost, you will find why fuses are used! Also, fuses will limit the peak current and probably open in less than half a cycle - limiting current squared x time to be born by transfo and its connections. A breaker will take several cycles, plus relay detection time.

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Dec 2009
Posts: 247
#2
In reply to #1

Re: Unit Auxiliary Transformer Protection.

08/21/2011 2:06 AM

about what percentage is kept for unit auxiliary transformer rating from that of generator rating?

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#3
In reply to #2

Re: Unit Auxiliary Transformer Protection.

08/21/2011 9:11 AM

Auxiliary loads are about 1% - 2% of unit rating.

The rating of the auxiliary transfo may depend more on the peak current during motor starting (voltage requirements for motor start) than on the running loads.

By keeping the peak current down, sequencing some of the motor loads can give a beneficial reduction in cost and space requirements of aux transfo.