Short Circuit Rating

07/18/2011 5:05 AM

I have done the Short Circuit Study for the MCC, and from the calculation the I"k = 82 kA, while the I'k = 74 kA.

Is it mandatory to use 100 kA MCC or I can just use 80 kA MCC instead?

Register to Reply
Pathfinder Tags: Short Circuit Rating for MCC
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Feb 2011
Location: Pune, Maharashtra, India
Posts: 32
Good Answers: 2
#1

Re: Short Circuit Rating

07/18/2011 10:52 AM

as per IEC-60909-0 there is I"k I.e. Initial symmetrical short circuit current (rms) and it does not define I'k. Please clarify/recheck. However, IEC defines ip i.e. Peak short circuit current. Switchgear components shall be selected as per initial symmetrical short circuit current as well peak SC current. Eg. If your short circuit level is 50 kA then your peak SC become 50*2.1=105kA. I.e. ACB/MCCB shall be suiutable for rated fault level of 50 kA and also for peak SC level of 105 kA. However, bus bars / bus ducts shall be designed as per rated fault level I.e. In our case 50 kA. Switch gears are defined in terms of rated service SC breaking capacity Ics, rated ultimate SC breaking capacity Icu, and rated short time withstand current Icw. A best selection of switchgear is Ics=Icu=50kA in our case. Icw is applicable for switch gears of utilisation category B I.e. Those having settable time delay (eg. ACB). Icw shall also be 50kA for 1sec of switchgear selected, in our case. There is also rated short time making capacity Iqm (peak value) = k x sqrt(2) x I"k in this equation k is R/X ratio of system k=1.02+0.98e^(-3R/X). In summary for MV system Peak SC factors to I"k are 2.54 for MV systems, for systems with fault current unto 50kA it is 2.1 and for above it is 2.2 times. Now you can do selection of your switchgear once you calculate fault current. As u know selection of MCC is having to aspects 1 selection of switchgear and 2 selection of switchgear. Hope I have answered your both questions...!

__________________
Engineering is an APPLICATION..
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Short Circuit Rating

07/18/2011 12:56 PM

What method did you use the calculate the fault current?

Register to Reply
Commentator

Join Date: May 2011
Posts: 80
#3

Re: Short Circuit Rating

07/18/2011 10:51 PM

@Salunkhem: Actually it's Ik, Steady-State Short Circuit Current. That means I have to use the 100kA panel then. I have increase the transformer impedance from 6% yo 9%, but the short circuit level is still more than 80kA. Is there a cheapest method to bring down the I"k slightly below 80kA?

@wareagle: The method is IEC 60909, exclude the Duty Calc.

Register to Reply
Associate

Join Date: Feb 2011
Location: Pune, Maharashtra, India
Posts: 32
Good Answers: 2
#4
In reply to #3

Re: Short Circuit Rating

07/19/2011 9:04 AM

Can you send your single line diagram on personal mail provided by cr4 I will have a look at it and crosscheck the results and let you know the solution. Prima-facie there seems to be something not appropriate. And yes, IEC itself said that, there are only two methods per unit and actual impedance calculation, whichever you do you should get same answer.

__________________
Engineering is an APPLICATION..
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#5
In reply to #3

Re: Short Circuit Rating

07/19/2011 9:35 AM

Move your MCC farther from your transformer. The longer cable length will provide more impedance, and the fault level at the MCC will be lower. You would have to rework your analysis to find out how far, but it's been done before.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#6

Re: Short Circuit Rating

07/19/2011 12:25 PM

I know of one situation where the engineer just looped cable around the transformer vault until he had enough impedance to drop the fault current to the value he wanted. That may be the cheapest way for you to do it. Similar to PeterT's suggestion.

Register to Reply
Commentator

Join Date: May 2011
Posts: 80
#7

Re: Short Circuit Rating

07/20/2011 5:33 AM

I've read about using a Fault Current Limiter between the Transformer and MCC. The question is what would be the final kA rating? Because the specification only mention about the kA Rating (120 kA which is way bigger than the MCC kA rating of 80kA) and the load ampere.

Is there somebody have an experience with Fault Current Limiter or Reactor to limit the fault current?

Regards

Register to Reply
Associate

Join Date: Feb 2011
Location: Pune, Maharashtra, India
Posts: 32
Good Answers: 2
#8
In reply to #7

Re: Short Circuit Rating

07/20/2011 9:13 AM

Yep in one of power plant supplied...

__________________
Engineering is an APPLICATION..
Register to Reply
Commentator

Join Date: Sep 2009
Location: Singapore
Posts: 77
Good Answers: 1
#9

Re: Short Circuit Rating

01/13/2012 12:03 PM

As what I read Ikmax (maximum steady state shortcicuit current) is used to determine minimum device rating. I don't see the sense! because I will rather choose of course I"kmax to determine max. device rating and this is the big deal to me not the min. device rating.

Ikmin (minimum steady state short circuit) used in setting of relay or protection

Ik"max, Ikmax, I"kmin and Ikmin is define by cmax & cmin factor in IEC 609090-0

One thing I"k is not used in comparing Device Duty, I"k is used to determine Ib and Ip and these are what we need.

Register to Reply