Does anyone know, which IEC standard to be used for Relay and Protection Coordination?

I have read NEC which specify this requirement, however I want to have some reference from IEC or DIN VDE. I tried Google, but no answer.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Relay and Protection Coordination

08/01/2011 7:33 AM

Please see IEC 60947-4 which defines two types of Co-ordination between an overload relay and the short-circuit-protective-device. Only refers to motor protection.

Do you mean something else?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Member

Join Date: Jul 2011
Posts: 7
#2

Re: Relay and Protection Coordination

08/01/2011 7:47 AM

Actully I was looking for protection coordination in LV system of power plant or critical loads.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: Relay and Protection Coordination

08/01/2011 8:02 AM

The IEC spec is one particular part of critical load protection, but if you think about it, all co-ordination (discrimination, cascading, etc) are similar in their objective viz. Isolation the faulty part with minimal disruption of power.

You can get lots of information from manufacturers on this, for example:

http://www.epowerengineering.com/guides-view-only.shtml

ECT 167

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #2

Re: Relay and Protection Coordination

08/01/2011 9:52 AM

Have you referred to IEC 60255? And, IEEE 242?

Register to Reply
Member

Join Date: Jul 2011
Posts: 7
#5
In reply to #4

Re: Relay and Protection Coordination

08/01/2011 10:11 AM

Yaa, I have gone through IEEE standard, but it does not directly address coordination requirement and issues related to LV distribution system. This has been addressed in NEC.

I want to refer IEC before going ahead with my design

I yet to refer IEC 60255, I will have a look to it.

Shridhar Sir, many thanks for the link.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6
In reply to #5

Re: Relay and Protection Coordination

08/01/2011 10:28 AM

You are welcome, glad to have been of some help. You will get many more similar documents from reputed manufacturers like Siemens, ABB Eaton, LSIS and so on. Good luck.

__________________