Previous in Forum: 110kv SF6 Breaker   Next in Forum: Combiflex Relay
Distance Protection(21)
08/02/2011 2:15 AM
for distance protection using Areva make Micom P444 relay -
1> the zones(1-2-3-P-4) are parallilopiped shape. what is the requirement of zone-P and how R_max and X_max settings are calulated?
2> Is it directional distance protection i.e. mho type?
3> what is memory polarisation and cross polarisaion? in P444 what type of polarisation use?
Re: Distance protection(21)
08/02/2011 2:17 AM
No hablo inglés.
Good Answers: 181
08/02/2011 4:23 AM
Try asking the question again giving some reference to the acronyms you have used.
Your post is total gibberish as it is.
Good Answers: 131
08/04/2011 1:18 PM
Sorry TonyS, but the OP's questions were pretty clear and unambiguous with respect to transmission line protection relays of the zone-distance or impedance type. Yes, it can seem like gibberish, but he wasn't like many posters who use abbreviations and acronyms, presented in fractured English or even text-speak. Unfortunately, my own experience is only enough to know that his question is clear, but not enough to give him a worthwhile answer.
Anonymous Poster #2
Re: Distance Protection(21)
08/02/2011 7:52 AM
Good Answers: 131
08/05/2011 9:17 AM
If you have to ask these questions, you are not qualified to program the settings for this relay. You need a course in transmission line protective relaying. I will give you what direction I can on your questions, but you have some research & study to do. There is some good info here:
http://store.gedigitalenergy.com/FAQ/Documents/L90/GER-3966.pdf
1. Zone P is programmable if you want an additional forward or reverse zone beyond the standard 3 forward and 1 reverse. The relay manual (link give by another poster) will explain its range and parameters. R and X settings are calculated based on your transmission line and fault parameters, just as you would for zones 1-3.
2. It is a quadrilateral distance-type relay. Mho-distance has a circular zone characteristic. Check out this link:
http://power-systems-protection.blogspot.com/2011/01/quadrilateral-characteristics.html
3. I'm not familiar enough with this relay to have any input here. The manual should tell you.
Good luck!
Anonymous Poster (2); PeterT (2); TonyS (1)