Previous in Forum: Megger Testing   Next in Forum: Question About Transmission Line Model
Close
Close
Close
2 comments
Rate Comments: Nested
Commentator

Join Date: Mar 2011
Location: off the beaten track, not quite whoop whoop nor humptydoo
Posts: 57

Earthing Gensets (Revisiting Thread �8929)

08/04/2011 2:04 AM

In previous post http://cr4.globalspec.com/thread/38929/Should-Mobile-Power-Generators-be-Grounded garth refers to a paper (http://www.wtia.com.au/pdf/TGN-W-05%20Earthing%20of%20mobile%20generating%20sets.pdf) that states to not fit an earth electrode to the mass of earth on portable gensets. This makes the genset functional earth connection 'floating', and an IT earthing system. (?An IT earthing system still has a connection to the mass of earth at the load side of the installation.?) Can someone please help me learn why?

I am trying to apply this (in Australia) to a specific scenario of a vehicle mounted genset (240v single phase, 16KVA). Each circuit is controlled by a double pole switch and protected by a GFCI. The earth conductors are bonded to the frame/chassis of the vehicle. Of primary concern is the potential harm to a person in the event of a fault if they are standing alongside the vehicle and they complete a circuit to the ground upon which we stand.

Possibly I just do not understand any of this, but not from a lack of trying...

__________________
Everything works out in the end, just not neccessarily how you want
Register to Reply
Pathfinder Tags: earth vehicle
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Earthing gensets (revisiting thread �8929)

08/04/2011 3:20 AM

If the genset is earth bonded to the chassis of the vehicle then definitely drive in an earth spike.

Have a look at http://en.wikipedia.org/wiki/Earthing_system

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#2

Re: Earthing Gensets (Revisiting Thread �8929)

08/04/2011 11:48 AM

If the genset is not referencing earth, there is no complete circuit.

This is why a poratable generator does not need to be grounded in order to run, and it doesn't shock people.

Your vehicle already has an alternator in it (generator, whatever) and your car is not grounded, right?

Now, if you are powering a building using this portable genset and it has a panel which references a ground rod for the building, the genset should be bonded to the same ground (or have its own ground rod bonded to the buildings ground rod) in order for the overcurrent devices in the building to function properly.

Register to Reply