Miniature Circuit Breaker

08/06/2011 6:19 PM

hi everyone,

i want to know the rule for selecting an MCB/MCCB for a given load i.e. of what rating MCB/MCCB should we select for a given load. say my load is 34 A , then of what exact rating MCB/MCCB should i use? . i know that the selected MCB/MCCB rating should be higher than the load current . but how much ?

regards,

Register to Reply
Pathfinder Tags: circuit breaker
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: miniature circuit breaker

08/06/2011 11:48 PM

1. What kind of a load? Motor, transformer, capacitor, resistance furnace, induction furnace, incandescent lights, flourescent lights, .....?? Each type of load has its own characteristic, and requires carefully coordinated protection.

2. Overload protection - selected depending on the type of load as stated above.

3. Short-circuit protection - depends on your supply system.

4. Earth-fault protection - depends on your overall system layout.

This is a complicated process, you would need to educate yourself on what is an MCB and an MCCB, how are they different, what types are there...so on. Plenty of stuff on the web.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#3

Re: Miniature Circuit Breaker

08/08/2011 12:08 AM

while going through the process described by KVShridhar you will also do well to remember . . .

that the source and devices upstream of the MCB or MCCB in question should also be studied to know the system fault level and whether the upstream devices are correctly selected for the fault current . . . if this care is not taken then possibly the protection may be inadequate.

Register to Reply
Associate

Join Date: Jul 2011
Posts: 48
Good Answers: 1
#4

Re: Miniature Circuit Breaker

08/08/2011 4:16 AM

Hi

As you say the rating of the circuit breaker should be higher than the load, but lower than the cable maximum current for the installation method used. In general terms, you would select the next rating up from your load, so in this case a 40A.

But as others have said you need to consider the type of load, from which you would select the tripping curve of the MCB (B/C/D) and you have to ensure it is capable of safely clearing the fault during a short circuit, that is its fault rating is higher than the circuit prospective fault current.

Register to Reply