what are the steps of synchro check for transmission line connected to grid?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: Synchro Check

08/09/2011 8:01 PM

The synch-check relay determines the condition of synchronization of the both side of the feeders and take the decision to allow closing the breaker. A synch-check relay first checks the voltage difference, frequency difference and the phase angle between the both side of the feeder. If these values are within the pre-setting values of the relay, the synch-check relay allows closing the breaker, otherwise it prevents the closing.