Capacitor Connections In Capacitor Bank

08/13/2011 10:16 AM

Dear CR4 users, i need small clarification In capacitor bank (which we are using for reactive power compensation) manufacture (L&T) has connected 3 capacitors in delta connection. Can this capacitors be connected in star connection with neutral. According to my analysis i think star with neutral is better, it increases the life of capacitor bank by avoiding circulating currents in capacitors.

__________________
key questions why, what & how - just think
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#1

Re: capacitor connections in capacitor bank

08/13/2011 10:38 AM

Yes. It would probably increase capacitor life but that's because of the lower voltage at which each capacitor is loaded. But also effective KVAR would decrease accordingly so you must then use bigger capacitors for same PF correction. So where is the gain? S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Associate

Join Date: Aug 2011
Location: India
Posts: 29
Good Answers: 2
#2
In reply to #1

Re: capacitor connections in capacitor bank

08/13/2011 11:19 AM

Voltage rating part advantage is OK. However, the kVAR rating will remain same irrespective of whether capacitors are Star connected or Delta connected.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#4
In reply to #2

Re: capacitor connections in capacitor bank

08/13/2011 11:46 AM

Er... are you sure? If the same capacitor bank (originally connected in Δ) is reconnected in Υ, the kVAR rating will become 1/3, i believe?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Associate

Join Date: Aug 2011
Location: India
Posts: 29
Good Answers: 2
#5
In reply to #4

Re: capacitor connections in capacitor bank

08/13/2011 1:08 PM

Let me try explain why I felt capacitor kVAR remains same:

Capacitor being source of reactive power, defined in terms of kVAR, i.e. it depends on V and I. While for delta, Vph=VL, for star Iph=IL, thereby 'advantage' gained by delta in V gets nullified by 'advantage' gained by star in I. Thus output kVAR remaining the same i.e. capacitor rating is independent of capacitor bank connection.

An analogy - For DY transformer, transformation from delta to star doesn't change the rating of transformer.

I am eager to learn, how capacitor bank kVAR rating gets reduced in Star connection.

Register to Reply
Associate

Join Date: Aug 2011
Location: India
Posts: 29
Good Answers: 2
#6
In reply to #4

Re: capacitor connections in capacitor bank

08/13/2011 1:50 PM

Oh, I missed same capacitor, whereby capacitance 'C' or capacitive reactance 'Xc' is already dead and frozen. Yes, I agree with you. The rating will go down by 1/3 as per formula given by wareagle below.

If still at design stage, kVAR rating will have no effect whether capacitor connected star or delta. Is that right ?

Register to Reply
Associate

Join Date: Aug 2011
Location: India
Posts: 29
Good Answers: 2
#8
In reply to #4

Re: capacitor connections in capacitor bank

08/13/2011 2:39 PM

Still on it. Pl. see the following link:

http://www.nepsi.com/del_new.htm

Capacitor: Except for voltage rating, the capacitors in both ungrounded-wye and delta-connected banks are the same and will have the same kvar rating.

Forum experts' views are requested.

Register to Reply
Commentator

Join Date: Sep 2008
Location: India
Posts: 91
Good Answers: 6
#10
In reply to #8

Re: capacitor connections in capacitor bank

08/13/2011 3:35 PM

Except for voltage rating, the capacitors in both ungrounded-wye and delta-connected banks are the same and will have the same kvar rating.

Yes you are correct.But you have to raise the line voltage by √3 times, so that the capacitors would get the rated voltage.

Otherwise kvar of individual capacitor would be 1/3 times. Kvar of capacitor bank would be 1/√3 times .

Register to Reply
Commentator

Join Date: Sep 2008
Location: India
Posts: 91
Good Answers: 6
#11
In reply to #10

Re: capacitor connections in capacitor bank

08/13/2011 4:06 PM

Sorry, a correction.

Otherwise kvar of individual capacitor would be 1/3 times. Kvar of capacitor bank would be 1/√3 times .

Register to Reply
3
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: capacitor connections in capacitor bank

08/13/2011 11:23 AM

The kvar rating is directly related to the voltage². A reduction in voltage will result in a significent recuction in KVAR. You would have to install additiional KVAR units to maintain you power factor. I do not see the advantage you are suggesting.

Known Variables: Capacitor Frequency, Capacitance, and Voltage Rating


Register to Reply Good Answer (Score 3)
Anonymous Poster #1
#17
In reply to #3

Re: capacitor connections in capacitor bank

08/14/2011 5:01 AM

The kV in formula is the system volg, which remains same, whether star connct or delta connct.

For say 6.6kV system, volg value in the formila will be 6.6 kv irrspective bank star connct or delta connect. it is not that for delta we put 6.6kv, for star we put 6.6/sqrt3 in the formula.

kVAR should remain same in both cases.

OP can provid more data, sys volg, cap design volg, kvar calculation etc.

Register to Reply Score 1 for Off Topic
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#18
In reply to #3

Re: capacitor connections in capacitor bank

08/14/2011 5:08 AM

Sorry I came in late for this topic discussion.

The KVAR consumed is directly proportional to square of the voltage applied as mentioned in this post.

Rating is related to capability. So if the Delta connected capacitors are connected in Star, their rating will not change, but their kVAR consumptions will change as the voltage across them will be different.

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#7

Re: Capacitor Connections In Capacitor Bank

08/13/2011 2:34 PM

Quote " If still at design stage, kVAR rating will have no effect whether capacitor connected star or delta. Is that right ?"

If you at the design stage, You call for a kvar rating at the voltage you have. Eg

you need 1000 kvar at 240 volts and you get 1000 kvar. If you need 1000 kvar at

208 volts you get 1000 kvar. The units are designed to work at the voltage you call for. Does that clear up your question?

Register to Reply
Associate

Join Date: Aug 2011
Location: India
Posts: 29
Good Answers: 2
#9
In reply to #7

Re: Capacitor Connections In Capacitor Bank

08/13/2011 2:54 PM

Pl. see # 8.

Register to Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#12

Re: Capacitor Connections In Capacitor Bank

08/13/2011 4:58 PM

I truly hope some guys giving answers here are not licenced engineers, because I cannot justify an engineer's ignorance in so basic concepts. When you buy KVARs you buy KVARs at a specific rated voltage (and frequency). This voltage has not only to do to capacitor's voltage tolerance, it is a part of the KVAR value itself. A 20 KVAR capacitor rated at 440v for example if connected at 220V same frequency, will give you 5 KVAR. If you can't understand this much, you're on a wrong line of expertise, sorry. S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Commentator

Join Date: Sep 2008
Location: India
Posts: 91
Good Answers: 6
#15
In reply to #12

Re: Capacitor Connections In Capacitor Bank

08/14/2011 12:32 AM

Hi simpleMind,

I have written in the sense that,

A 20 KVAR delta connected capacitor bank at 440V would have the same KVAR rating if star connected at 440*√3= 762V, so that individual capacitors get 440V. By this way i mean that, as the system voltage is constant, the KVAR rating of capacitor bank would be only 1/3 times when star connected.

Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#13

Re: Capacitor Connections In Capacitor Bank

08/13/2011 7:42 PM

Qoute Hbadham "Capacitor: Except for voltage rating, the capacitors in both ungrounded-wye and delta-connected banks are the same and will have the same kvar rating."

I see where the confusion is now.This statement is saying that if you have 1000 kvar connected delta and 1000 kvar connected wye you will have the same kvar rating of 1000 kvar. They will have the same effect on your utility bill. But the delta kvar units will not work on a wye system. The units are designed to provide 1000 kvar at the voltage rating of the system to which they are connected. Therefore when you are designing a system to use capacitors, you must specify the system voltage to get the correct KVAR rating. On a delta system the units are connected phase to phase. On a wye system they are connected phase to neutral.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#14

Re: Capacitor Connections In Capacitor Bank

08/13/2011 10:55 PM

i think this thread has become a hapless victim of the semantic barrier in communication like a delta connected capacitor when confronted with the dreaded triplen currents . . . goes round and round and only creates heat in the process . . . .

to confound the matter now i suggest using a capacitor set rated 900kVAR at 718 V in delta on the same 415V bus to get the same PF benefit and increase capacitor life . . .

go drive a Beamer series 7 behind a Suzuki Swift in Madison Avenue or Zaveri Bazaar afternoon traffic and sing hakuna matata . . .

Register to Reply Score 1 for Good Answer
Associate

Join Date: Jul 2011
Posts: 34
Good Answers: 1
#16

Re: Capacitor Connections In Capacitor Bank

08/14/2011 4:10 AM

A good way to understand this is to consider wye/delta starting of motors. Emphasis must also be placed on rated vs applied voltage. With the supply voltage (line to line) the same, the voltage seen by the motor windings is dependent on how it is connected-wye or delta. Take the case of a motor rated to deliver its HP (horsepower) rating with the rated voltage applied and the motor connected in delta, if you start the motor in wye and keep it running that way, it will burn out because it is attempting to deliver its HP rating at a lower voltage across its windings- resulting in current above its rated full load current.

A "similar" reasoning applies to the capacitor banks; you get reduced voltage across the capacitors in wye and cannot expect to get the rated KVAR.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Aug 2011
Location: India
Posts: 29
Good Answers: 2
#19

Re: Capacitor Connections In Capacitor Bank

08/14/2011 8:35 AM

Yes. Just like AH capacity of a battery bank (analogous to capacitor rating), its full AH 'nameplate' rating is of no use if battery cannot be charged to its full capacity (analogous to capacitor bank which cannot be charged to its 'full potential' due to reduced volg. available in star). Excellent postings at # 3, 13, 16 (nice analogy) & 18.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#20

Re: Capacitor Connections In Capacitor Bank

08/16/2011 11:18 AM

Please remeber that in Delta connection, even a smaller cell capacitance would give a better equivalent capacitance across the two lines. Say, in a three phase delta connected capacitor, the net capacitance across lines 'R' & 'Y' would be 1.5 C, where 'C' is the individual cell cpacitance. Remember, it is a series parallel circuit. So, also for the other two lines 'Y-B' and 'B-R'. Thus, you get a better kVAR output for a smaller cell capacitance.

Whereas in Star connection, you would only get 0.5C across any two lines, where 'C' is the individual cell capacitance. (It is only a series connection now).

So, if you re-connect the alreday delta connected capacitors in star, you would get only 1/3rd of the kVAR output of that in Delta.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#21

Re: Capacitor Connections In Capacitor Bank

08/16/2011 7:07 PM

As for as connection in Star is concerned it is quite safe electrically but what difference it makes the system is questionable.

Register to Reply
Register to Reply 21 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!