What is the significance of a fault MVA. How does it effect systems stability.
We have 110kv substation with 1327 fault MVA on 110kv bus. A 16 mva with z=10.34%; transformer (110/33) is connected. A 33 kv substation connected 6.5 km away from our substation. Help me to find fault mva on 33 kv substation.dog (overall dia 14.4mm)conductor is used in 33 kv line.
Good Answers: 181
Re: Fault MVA
08/28/2011 4:37 AM
Ever tried doing your own homework?
Re: Fault MVA
08/29/2011 10:20 AM
will u help me?
Re: Fault MVA
08/28/2011 8:12 AM
Google "Short Circuit ABC--Learn It in an Hour" and spend that one hour.
Re: Fault MVA
08/29/2011 6:18 AM
Tedious calculations, but, I can give you the data.
According to me,
Fault level at Inlet of your 33kv sub station after 6.5 km from 110kv/33kv sub station will be
Ifault - 2.66 KA . Fault MVA = 152.
This data will be useful in setting the Protection relays in your in comer circuit breaker. If properly set, breaker will provide perfect protection to the line / system. Other wise, Breaker some times will not trip during faults.