440 V Power Distribution

08/29/2011 5:59 AM

Dear all

In 440 V 3 phase 4 wire system, can we made multiple neutral earthing at each load centre, instead of common neutral at transformer ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: 440 V Power Distribution

08/29/2011 9:17 AM

Yes, BUT not recommended. What you're suggesting would be a big PME system.

If you have good neutral and CPC conductors why would you want to do this?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#2

Re: 440 V Power Distribution

08/29/2011 1:45 PM

Perhaps... the answer to this depends upon where you are in the world.

If you are in North America (Canada or the US), the answer is no. The neutral of each separately derived system is to be tied to ground in only one location. This is accomplished by connection to its own grounding electrode (in which case all of the electrodes at a facility must be interconnected) or by connection to a common grounding conductor that runs to the main service grounding electrodes.

Also important... the bonding system for each separately derived system also starts at the point where the neutrals are connected to the grounding system.

Connecting the neutrals to ground in more then one location sets up possible multiple return paths for fault and imbalance current. This could cause a potential difference across the different bonding systems. Not a a good thing...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".