Line Side Protection of Substation at Powerhouse

08/30/2011 12:37 AM

I have seen cases, where one set of three core and one set four core CTs are connected in the line side of transmission line from the substation of powerhouse (i.e. going outside from busbars towards the load). eg. 400-200/(1-1-1A) and 400-200/(1-1-1-1A).

But sometimes, double core CTs are also used. 500-250 / 5 A.

Of course, the correct no. of cores and numbers depend upon the scheme of protection adopted. But what is normal practice?

Regards,

sks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: Line Side Protection of Substation at Powerhouse

09/01/2011 2:10 PM

There is no single "normal practice." What is used for # of CTs and # of cores depends on the protection schemes used and the protection and design philosophy of the engineer(s) doing the design, and also any codes or design criteria which may be mandated by regulatory bodies that have oversight of the transmission system.

Sometimes it is accepted that different redundant protection systems can use different cores of the same CTs, but other people or design requirements call for them to be on different CTs. Some people allow metering or SCADA circuits to be on the same CTs, even the same CT secondary, as protection circuits, while others require them to be separate.

__________________
To get the right answers, first you need to ask the right questions.