About Induction Motor

09/02/2011 5:26 AM

Dear friends,

My friend had purchased induction motor & variable frequency drive from two different suppliers.

Motor rated speed is 1000 R.P.M, he tried to run the motor at 120 R.P.M using Variable frequency drive but vibration is coming from motor.

what may be the problem?

Can't we run a Induction motor of 1000 R.P.M into 120 R.P.M?

or

Drive problem?

or

Motor Problem?

What is the minimum speed & maximum speed, we can run from 1000 R.P.M motor using V.F.Drives?

With regards,

Amith N

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Associate
India - Member - New Member

Join Date: Oct 2009
Location: INDIA
Posts: 49
Good Answers: 1
#1

Re: About induction motor

09/02/2011 5:53 AM

May i know the make of drive and mobel number

__________________
key questions why, what & how - just think
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: About Induction Motor

09/02/2011 12:37 PM

There should be no problem with regards to vibration as far as running the motor from the VFD, assuming the VFD is properly programmed. Before you assume that anything else is the problem, you need to make sure the VFD is properly programmed for the motor nameplate data and the power supply.

But there are sometimes issues with mechanical resonnance when running LOADS at specific speeds, we call them "critical speeds". The VFD can usually be programmed to disallow having those specific speeds or ranges of speeds selected by operators. It responds by either staying lower or moving higher, you get to decide.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Associate

Join Date: Mar 2011
Posts: 48
#3
In reply to #2

Re: About Induction Motor

09/02/2011 12:50 PM

if there is a parameter on the drive for motor winding resistance,then check that one.

if u enter wrong motor resistance that time this prob may be occur

Register to Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#4

Re: About Induction Motor

09/02/2011 7:49 PM

Inverter programming has vendor specific approaches ,so it would help to have the inverter type to advise. And if you are constantly working at low band like 6Hz don't expect your motor to give rated torque for serious duty cycle because of overheating risk. Anyway first check your V/F pattern's low end for programming errors like min voltage etc, stall prevention parameters, and of course motor related parameters. S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5
In reply to #4

Re: About Induction Motor

09/02/2011 9:40 PM

Ooooh, 6Hz... I didn't do the math. You're right, that's very very slow.

What he said.

And if the VFD is not at least a "Sensorless Vector Drive", speed regulation below 4:1 is going to be very poor. You are at a tad over 8:1 turn down.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#6

Re: About Induction Motor

09/02/2011 11:17 PM

do you have a 2 pole or 4 pole motor?

to run that low you will need a 4 pole motor, if you have a 2 pole motor, the rpm you want can cause vibration as you are not achieving or at the threshold of the start Hz/rpm for the motor if under load.

__________________
The square root of nothing is what you make it!
Register to Reply
Associate

Join Date: Aug 2011
Posts: 41
Good Answers: 7
#8
In reply to #6

Re: About Induction Motor

09/03/2011 12:05 AM

OP has already mentioned 1000 rpm motor, it's a 6 pole motor. To further reduce the rpm he has to introduce a gearbox or a belt drive. here I want to ask some more information from OP, as vibration can be due to several reasons.

1. What load is coupled with motor which is is required to be run at 120 rpm?

2. How it is coupled, whether it is properly aligned?

3. Whether high vibration occurs through out the range of speed or at particular speed bands?

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#10
In reply to #8

Re: About Induction Motor

09/03/2011 12:28 PM

I see no mention of 6 poles..... are you assuming its a 6 pole motor?

I NEVER assume, as it can and has caused all kinds of screw ups...

Assumption is the Mother of all F£$% up's

Its good to remember that!

__________________
The square root of nothing is what you make it!
Register to Reply Score 2 for Off Topic
Associate

Join Date: Aug 2011
Posts: 41
Good Answers: 7
#11
In reply to #10

Re: About Induction Motor

09/04/2011 5:10 AM

Dear brich, I am not assuming the number of poles. But, you are right, I assumed frequency as 50 Hz. It's a simple assumption as explained below:

Motor speed (rps) = 2 x Frequency (Hz) / number of poles

Motor speed (rpm) = 120 x Frequency (Hz) / number of poles

So, for 50 Hz frequency:

Motor speed (rpm) = 3000 (for 2 pole motor)

Motor speed (rpm) = 1500 (for 4 pole motor)

Motor speed (rpm) = 1000 (for 6 pole motor)

For 60 Hz frequency above figures are 3600, 1800 and 1200 rpm respectively. As OP says 1000 rpm, I assumed 50 Hz frequency with 6 pole. Hope you will appreciate my assumption.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#12
In reply to #11

Re: About Induction Motor

09/04/2011 7:23 AM

I don't need you to teach me mathematics.... if the OP can't be bothered to give ALL the information, then I can't be bothered to work out what he's trying to say.

What happens to your calculations if it's 60Hz?

Don't assume.. plain and simple.. and don't try to teach me how to count, there's a good boy!

And just reading your reply AGAIN before I post this.......you are assuming

__________________
The square root of nothing is what you make it!
Register to Reply Off Topic (Score 6)
Associate

Join Date: Aug 2011
Posts: 41
Good Answers: 7
#14
In reply to #12

Re: About Induction Motor

09/04/2011 12:33 PM

But, you are right, I assumed frequency as 50 Hz.

Dear Guru brich, respectfully I want to say that you need to to be taught mathematics. It's simplest manner, I explained, but you could not understand. I have clearly explained, what will be the speeds, if it's 60 Hz. OP's motor speed doesn't fit in to resultant speeds of 60 Hz frequency. So, its clear, it must be 50 Hz.

And, please don't say me again "Don' assume". I will keep on assuming, whenever I like on such things, which will be useful. I didn't try to teach you how to count, I tried to clarify that OP's motor must be a 6 pole motor, which is slower than 4 pole you was suggesting. See below your own post, will you not laugh over it.

"do you have a 2 pole or 4 pole motor? to run that low you will need a 4 pole motor, if you have a 2 pole motor"

Register to Reply Off Topic (Score 3)
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#16
In reply to #12

Re: About Induction Motor

09/06/2011 10:07 AM

Birch, With all due respect and a hearty agreement on your implied definition of Ass-U-Me, the OP did say the motor rated speed was 1000 RPM, not the driven speed. So 50 Hz is implied almost exclusively, with the sole possible exception of it being a VERY high slip 6 pole 60Hz motor and I have never seen one with 17% slip.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#18
In reply to #16

Re: About Induction Motor

09/06/2011 12:59 PM

thank you..with the greatest amount of respect.....yes I know its calculates out to be a 6 pole..but my reply was to state that one MUST assume nothing... and for the purpose of our other member who took it upon himself to teach me how to calculate, I had already completed the calculations, and my statement of "4 pole motor" was an attempt to illicit a further response from the OP, who like so many is very conspicuous by his absence, to see if he's on the ball, knows what he is talking about and he has ability to pick up on my statement AND give further info.

But and here it comes...But are the figures/facts correct from the OP? Using the OP's facts, then yes one can calculate that the motor is indeed 6 pole, on the figures given, the calculation is correct.

How many times have we sat at our respective computers, given an answer based on facts presented only to be informed by a dyslexic OP that he got the figures totally wrong..... so.. for me... no assumptions.. only facts!

The facts, the whole facts, and nothing but the facts.

__________________
The square root of nothing is what you make it!
Register to Reply Score 1 for Off Topic
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#19
In reply to #18

Re: About Induction Motor

09/06/2011 9:09 PM

Point well stated and understood.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Commentator

Join Date: May 2010
Location: UK
Posts: 89
Good Answers: 2
#13
In reply to #11

Re: About Induction Motor

09/04/2011 7:47 AM

so in your calculations you don't say what Hz is required to run the motor at 120rpm.. what is it?

If you are going to give an answer, please give a full one

Register to Reply
Associate

Join Date: Aug 2011
Posts: 41
Good Answers: 7
#17
In reply to #13

Re: About Induction Motor

09/06/2011 11:01 AM

My calculations is not for inventing new Hz other than 50 & 60. Getting 120 rpm is job of VFD.

Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#7

Re: About Induction Motor

09/02/2011 11:27 PM

Details please!

A good VFD with Sensorless Vector control or full vector control (with tach feedback) should be able to run this OK.

Is this vibration low frequency showing up in the drive train, or are you talking about a high frequency whine or buzz?

You need to give us make and model # and NP ratings for VFD and motor.

Drives like the ABB ACS800 or Rockwell Powerflex 700 series should be able to handle this type of application ie speed range. You may want a forced vent motor or TENV so that overheating is not a problem.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2007
Location: Mumbai, India
Posts: 1983
Good Answers: 25
#9

Re: About Induction Motor

09/03/2011 8:27 AM

Hi Amith,

Why you are replying to questions asked by experts?. Many a times OP ask questions and simply disappear.

__________________
"Engineers should not look for jobs but should create jobs for others" by Dr.Radhakrishnan Ex President of India during my college graduation day
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#15

Re: About Induction Motor

09/06/2011 9:34 AM

Normally it is possible to run any motor to lower speeds in the ration of 1:10 that is 100RPM theoretically.But in Practice u need to study the Torque speed curve for such low speeds.If the motor POT is below 200% of FLT then possibility of entering in the unstable (non linear)region cannot be ruled out and hence vibrations can occur.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Register to Reply 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

brich (4); GW (1); JRaef (4); loyd (1); nesubra (1); parvathaneni (1); pradeep44 (4); SimpleMind (1); suresh sharma (1); thccontrols (1)

Previous in Forum: Polling Station   Next in Forum: Request for Delta Connection Diagram

Advertisement