Duty Cycle of 33 kV Circuit Breaker.

09/06/2011 2:10 AM

i have come through occasion with the following operating sequence of 33 kV VCB:

Rated operating sequence (for auto reclosing) O - 0.3 sec - CO - 3 min - CO

in hydropower plant after 6.6 VCB, it is stepped up and 33 kV VCB is kept in powerplant. Does it require auto-reclosing. I think without auto-reclosing, it will be O - 3 min - CO - 3 min - CO.

sks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Duty Cycle of 33 kV Circuit Breaker.

09/06/2011 4:51 AM

Ask the person that designed the system. Auto re-closing isn't something that's done with out careful consideration. And unlikely in a power plant.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#2

Re: Duty Cycle of 33 kV Circuit Breaker.

09/07/2011 2:00 AM

The auto recloser is used for overhead power lines that are air insulated / gas insulated, the air/gas being a regenerative insulation. This is the only situation when an auto recloser is used. If the circuit breaker corresponds to a transformer or generator than the auto recloser has to be canceled. Without auto reclosing it won't be O-3min-CO-3min-CO, it will be just O ;) and this is done via the protection relay. When someone says that the circuit breaker has auto recloser it actually means that the breaker is just capable to operate an auto-reclosing cycle. For a breaker to work in the auto reclosing mode it needs a brain - the automation relay/logic to send the electrical impulse for auto reclosing.

tchuss

__________________
The time is ......now
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Dec 2009
Posts: 247
#3
In reply to #2

Re: Duty Cycle of 33 kV Circuit Breaker.

09/07/2011 2:37 AM

what dou you mean it will just be O ?? You mean no CO is needed? i.e. since there is no reclose so just open and finished?

As far as I understand, there are two rated operating sequences, defined by IEC and it gives 3 min for time for circuit breakers not intended for rapid auto-reclosing.

1. O-t-CO-t' - CO

2. CO - t" - CO.

sks

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4
In reply to #3

Re: Duty Cycle of 33 kV Circuit Breaker.

09/07/2011 7:16 AM

Most CB's just open on fault. Auto re-close is the exception to most operating situations. You may have the facility to set re-close in a protection unit, but 99% of the time you don't want it as it would be dangerous!

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#5
In reply to #3

Re: Duty Cycle of 33 kV Circuit Breaker.

09/07/2011 7:47 AM

Yes, there is just "Open" and finished, just as Tony told you earlier . The auto reclosing sequences are attributed to the actuator of the CB because the actuator has to be albe to perform the auto reclosing.

As far as I can tell you still have a lot to learn about power stations, and electrical equipment.

If there is anything else unclear from what I told you just say and I'll try to be as clear as possible in explanations.

tchuss,

nikolay

__________________
The time is ......now
Register to Reply
Associate

Join Date: Aug 2011
Location: India
Posts: 29
Good Answers: 2
#6
In reply to #3

Re: Duty Cycle of 33 kV Circuit Breaker.

09/08/2011 12:48 PM
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Dec 2009
Posts: 247
#7
In reply to #6

Re: Duty Cycle of 33 kV Circuit Breaker.

11/27/2012 3:59 AM

thanks friend, but it is all about ANSI/IEEE standards, and nothing to do about IEC standards. We are talking about IEC standad here.

Thanks,

sks

Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

hbadhan (1); nikolay (2); sauravbabu (2); TonyS (2)