Continuous Rating for Busbar Current.

09/10/2011 8:02 AM

what are the standard values of busbar current for substation of hydroelectric power plant eg. like 200A, 3150A, 4000A etc? what are the corresponding short circuit values?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Power-User
India - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Apr 2010
Location: Asia/India
Posts: 365
Good Answers: 1
#1

Re: Continuous Rating for busbar current.

09/10/2011 8:50 AM

The question should be like what should be the standard current rating of copper bar at so and so ambient temperature having so and so width and thickness?

Your second question need to be asked with more parameters included.

Register to Reply
2
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: Continuous Rating for busbar current.

09/10/2011 11:51 AM

The Indian practice is to use Renard R20 series of preferred numbers. i seem to recall the IS standards also mention this. Not mandatory, only recommendatory.

http://en.wikipedia.org/wiki/Preferred_number#Renard_numbers

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Good Answer (Score 2)
Associate

Join Date: Aug 2011
Location: India
Posts: 29
Good Answers: 2
#3
In reply to #2

Re: Continuous Rating for busbar current.

09/10/2011 12:33 PM

Thanks for this very useful link.

Register to Reply
Participant

Join Date: Jul 2011
Location: Nottingham, United Kingdom
Posts: 3
#4

Re: Continuous Rating for Busbar Current.

09/10/2011 4:50 PM

Hi,

There are a number of methods for giving guides to the bars rating, however they should only be used as guides. I have experience of significant changes in the ratings of bars the size of the bar alone is not enough to give you a figure.

The busbar current rating is dependent on a number of factors including; the assembly layout, the IP rating of the assembly however it can also be significantly affected by the supports of the busbars and the devices that the busbars are connected to.

IEC61439-1&2 are the applicable international standards for Low Voltage Switchgear and Controlgear Assemblies; it advises that unless certain specific conditions are met, the only way to be assured in the rating of the equipment is to perform verification tests.

Regarding the short circuit capability, we have developed an application for both Android and IPhone and IPad search for Transcalc, they are available free of charge. This application will inform you what the potential short circuit that can be produced by a transformer. The application also will calculate the busbar temperature rise expected to occur during the short circuit.

Have a look at these two companies website, one can provide technical support and one provides the testing service.

http://www.ka-testing.com

http://www.3phasedesign.com

I hope that this gives some guidance

Rob

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5

Re: Continuous Rating for Busbar Current.

09/11/2011 6:36 AM

I applaud you lads for sticking with this guy. You're saints

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

hbadhan (1); hithuanand (1); kvsridhar (1); robencompass (1); TonyS (1)

Previous in Forum: CT Polarity   Next in Forum: UTE C15-500 (Cenelec report R064-003)

Advertisement