PLC Mainframe Issue

09/11/2011 1:50 AM

After troubleshooting a AB PLC issue with no results, I have the following question. On Input bits 16 and 6 slots 1 through 4on a 2 slot address, the PLC does not recognize or accepts the signal. We have tried new input cards with no luck. We thought a mainframe was the problem. But we still have the same issue. What are we missing?

__________________
"It is what it it is."
Register to Reply
Pathfinder Tags: PLC
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: PLC Mainframe Issue

09/11/2011 8:15 AM

"... the PLC does not recognize or accepts the signal." How do you know this? Are you examining the inputs directly (using e.g. RSLogix), or otherwise? Are the monitoring indicator lamps lighting for these inputs?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#2

Re: PLC Mainframe Issue

09/12/2011 6:51 AM

Along with JohnG's questions, was the unit in service and quit working or are you just trying to program. If the later did you set-up the I/O card in the processor?

Also I assume that the main frame that you refer to is the processor!

Register to Reply
Associate
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Sep 2009
Location: Cincinnati, Ohio, USA
Posts: 29
#3

Re: PLC Mainframe Issue

09/12/2011 7:10 PM

We are using RSLogix5. The original install is about 11 years old. We have inputs on the input table from limit switches that are registeering a 0 when the input wire at the input card from the limit switch is checked with a Solenoid Voltage Tester, there is 120 vac. This is giving us closed faults on our open valves that we have to force on to show they are open in order to continue running. We tried new input cards are a new mainframe. We still have the problem. What is weird is that the input problems are all bit 6 or bit 16 on the input cards.

__________________
"It is what it it is."
Register to Reply
Associate
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Sep 2009
Location: Cincinnati, Ohio, USA
Posts: 29
#4
In reply to #3

Re: PLC Mainframe Issue

09/12/2011 7:14 PM

To add, the mainframe did include the processor and power supply. Which were both changed out. We were having power supplies drop out and decided to be proactive in this case.

__________________
"It is what it it is."
Register to Reply
Power-User
Engineering Fields - Control Engineering - Newby Member Long Time User Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jun 2006
Posts: 224
Good Answers: 9
#5

Re: PLC Mainframe Issue

09/13/2011 11:58 AM

One quick question and then possibly some follow ups: Do the LED indicators on the front of the input modules correctly show the state of the input?

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#6
In reply to #5

Re: PLC Mainframe Issue

09/13/2011 5:57 PM

... a question I've already asked, but it was not answered. CriscoKid?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Participant

Join Date: Sep 2011
Location: Tampa, Florida
Posts: 4
#7

Re: PLC Mainframe Issue

09/13/2011 7:56 PM

"..PLC does not recognize or accept the signal..."

Some things I would check:

1. Is your common wire at the input card loose? Is it a true neutral common?

2. Are the LED's in the input card lighting up when you receive power?

3. If you are monitoring through RSLogix, is the ladder for the section of logic you are using currently being scanned or is it being inhibitted by another condition?

4. If it is a remote rack, have you lost communication to your main rack?

Register to Reply
Associate
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Sep 2009
Location: Cincinnati, Ohio, USA
Posts: 29
#8
In reply to #7

Re: PLC Mainframe Issue

09/13/2011 10:42 PM

Sorry about the lamp question.

1.No, the lights do not indicate they are receiving power.

2.Yes, the nuetral is tight and a true nuetral.

3.We are using RSLogix5 and there are no inhibiters that are seen.

4.We also tried an auto config in RsLogix to make sure it was still there.

5.Not all bits are acting up. Some other inputs are just fine.

I work straight night shift so excuse the lateness on my replies.

__________________
"It is what it it is."
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#9
In reply to #8

Re: PLC Mainframe Issue

09/14/2011 2:07 AM

If the input indicator is not lighting, you can forget the PLC itself[1] and all software issues.

It's a hardware/wiring fault of some kind.

[1] Unless the input circuit of the PLC is faulty, which seems unlikely as it happens on several cards, including new ones. The remaining possibility here is that the PLC input circuits have all been damaged by overvoltage. Is this a possibility in your circuitry? What is the AB type number of the input card?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply