We manufacture LT power cables and face a problem as mentioned below.
The routine tests on Finished cables are; HV test (3kV AC for 5 minutes) & Conductor Resistance test. In certain occasions, our cables fail in HV test. We measure the Insulation Resistance of the failed cores and if the resistance is less than 1Megohm, we identify the fault using surge and TDR. If the fault is a high resistance fault, we are running out of options as the TDR is unable to locate the fault. We heard that bursting the cable could be the best solution. Is that true? If that is true what could be the required voltage / current that can be used to burst the cable? Can anyone suggest a solution?
Many thanks in advance....