Tap changing gear
i) Type
ii) Provided on
iii) Tap range
iv) Step Voltage
v) Rated voltage of on load tap changer
vi) Rated current of on load Tap changer
Over voltage operating capability and duration
Max flux density in any part of core and yoke at rated MVA ,normal voltage(Tesla)
Current density of HV /LV Windings
Insulation Levels for windings
a) 1.2 /50 micro - second wave shape impulse withstand (kVp)
b) Separate source withstand voltage (kV rms)
c) Power frequency voltage withstand (kVp)
Type of winding insulation
a) HV
b) LV winding
System short circuit level and duration for which the transformer shall be capable to withstand thermal and dynamic stresses (kA rms /Sec)
Noise level at rated voltage and frequency
Permissible temperature rise over ambient temp of 50 DC
i) Of top oil measured by thermometer
ii) Of winding measured by resistance
Minimum clearance in air (mm)
HV
a) Phase to Phase
b) Phase to ground
LV
c) Phase to Phase
d) Phase to ground
Terminals :
a) HV winding Line end
b) HV winding Neutral end
c) LV Winding
Bushing current rating
HV
LV
Max Radio Interference voltage level at 1 MHZ & 1.1 times max rms phase to ground voltage for HV Terminal Connector
Cooling Equipments
a) Number of Banks
b) No of Pumps
c) No of fans
Insulation level of bushings
a) Lightning impulse withstand (kVP)
b) Switching impulse withstand (kVP)
c) 1 Minute power frequency withstand voltage (kV rms)
d) Creepage distance (mm)
Bushing current transformers for purchasers use
(for restricted E/F protection)
i) Type
ii) Quantity
i) No of Cores
iii) Current Ratio (A/A): (A/A)
ii) Turn ratio
iv) Knee Point Voltage
v) Accuracy class
iii) Location for mounting
HV Neutral side CT for owners use
iv) Type
v) Quantity
vi) No of Cores
vii) Current Ratios (A/A)
viii) Turn ratio
ix) Knee point voltage
x) Class of accuracy
xi) Location for mounting
Bushing CT on LV side for load measurement
i) Type
ii) Current ratio
iii) Burden in VA
iv) Accuracy class
v) No of cores
LOSSES
Maximum acceptable (without any positive tolerance) no load loss (Iron Loss )at rated voltage and at rated frequency at 75 deg C in KW
Maximum acceptable (without any positive tolerance) load loss including cooler loss because of power consumption by the cooler fans ,motor pump sets etc at rated current and at rated frequency at 75 deg C in KW
Maximum acceptable (without any positive tolerance) Auxiliary Loss in KW
Re: how to calculate the parameters of a transformer specification
09/24/2011 4:47 AM
Did You mean design, as mostly parameters related to it.
09/26/2011 1:11 AM
Spec. of 80/100MVA step-up transformer is to be made to float it pls
United States - Member - Member Hobbies - DIY Welding - New Member
Good Answers: 50
Re: How to Calculate the Parameters of a Transformer Specification
09/25/2011 12:12 AM
So, do you have a question?
Speak softly and carry a big stick.
09/26/2011 1:10 AM
S pls.I need d procedure,formulae,......to find those mentioned 2 prepare a detailed spec. of a 80/100MVA ONAN/ONAF step-up transformer
Good Answers: 170
09/25/2011 11:47 AM
Please get a copy of IS or IEC or IEEE Standards on Transformer Specifications and religiously go thro it. You will, then be able to specify a transformer correctly.
09/26/2011 1:08 AM
Can u provide me the standards pls
09/27/2011 12:30 PM
IEC 60076 series is quite helpful. The J&P transformer handbook also provides good background
09/28/2011 1:14 AM
Thanku so much